The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102557 - 06/01/06 10:49 AM Service disconects for outbuildings
Jonno Offline
Member

Registered: 05/27/06
Posts: 20
I was working on a cottage recently, adding a few new circuits for a sump pump and washing machine and cleaning up some one else’s creative wiring.

The cottage has a detached shed, fed by a 3 conductor TEK, the original installer fed the TEK off of the living room lighting circuit, one of the conductors was a supply for the inside lights and plug, another was used as a switch leg so that the outside light on the shed was controlled by a switch in the living room. There is of course a neutral and EGC.

I moved the shed onto its own breaker. I was wondering on what everyone’s thoughts on how I could cover the service disconnect for this shed.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102558 - 06/01/06 10:07 PM Re: Service disconects for outbuildings
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
not sure what you mean by "cover the service disconnect for this shed"

Top
#102559 - 06/02/06 08:08 AM Re: Service disconects for outbuildings
Jonno Offline
Member

Registered: 05/27/06
Posts: 20
Sorry, my poor choice of wording.

I am asking for insight on how you would provide a service disconect for this shed.

Top
#102560 - 06/04/06 10:11 PM Re: Service disconects for outbuildings
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
You would not really have a service disconnect to an outbuilding,since what you are describing is a branch circuit off your main panel. What you may require, depending on how much power you are bringing to the outbuilding, could be some kind of sub-panel. Be sure to read CEC 10-208. You are allowed two 15 amp circuits to the outbuilding without a subpanel-but I cant find that rule, be sure to talk to your local AHJ to check local rules also.

Top
#102561 - 06/16/06 09:05 AM Re: Service disconects for outbuildings
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
I would look at this in two ways. If it is a home there would be no requirement for a disconnect at the shed and I might prefer to see a sub panel I cannot think of any reason that a person would be required to run a sub panel and feed the circuits from their.
Even a commercial application if the shed is not a seperate tennant then it could still be fed either via a sub panel or separate circuits. Now if the shed was functionally seperate IE a different tennant then a panel with a local disconnect would be in order.
In BC each occupancy must have a local disconnect within the occupancy.

Top
#102562 - 06/21/06 06:44 PM Re: Service disconects for outbuildings
Cosimo Offline
Junior Member

Registered: 06/21/06
Posts: 6
In Ontario this rule applies:
14-418 Disconnecting Means

(1) A single disconnecting means shall be provided either integral with or adjacent to the distribution equipment:

(a) Within each unit of a multi-unit building, other than a dwelling unit;

(b) Within each area common to more than one building, such as an underground parking area; or

(c) Within each building when fed from another building.

(2) Subrule (1) does not apply to circuits from part of fire alarm, fire protection and emergency systems.