The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102162 - 04/14/05 06:58 AM Welding Receptacles
Brad Offline
Junior Member

Registered: 04/13/05
Posts: 2
Loc: Winnipeg, Manitoba, Canada
Hello, I've got a request for a design (600V welding plugs that I'm having some trouble with.

The design calls for having 8 welding plugs available. The intent is that no more than two of these plugs be used at the same time. The request calls for 60 A plugs

I believe that the overcurrent protection for this system (in accordance with Canadian Electrical code Section 42-006 Sub 2) should be 256 Amps which would require 250 AWG wire.

This seems like an awful waste, as the intent is to run two welders max, but I'm not aware of any provisions that let you rate your welding supply based on intent.

Has anyone ran across a problem like this?

Thanks, Brad.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102163 - 04/14/05 05:36 PM Re: Welding Receptacles
Sandro Offline
Member

Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
Intent is one thing....actual use is another. I believe in future proof installs when reasonable and possible. Who is to say that down the road, not more than 2 receptacles will be used? What if more employees get hired, or they get super busy?

I'd run separate lines.

*** edited for spelling ***

[This message has been edited by Sandro (edited 04-14-2005).]

Top
#102164 - 04/15/05 07:02 AM Re: Welding Receptacles
Brad Offline
Junior Member

Registered: 04/13/05
Posts: 2
Loc: Winnipeg, Manitoba, Canada
I figured that'd be the way things had to work. Damned logic!

Thanks, Brad.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals