The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 108 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102107 - 02/12/05 01:34 PM Can you settle a dispute?
Charles Offline
Member

Registered: 10/09/03
Posts: 60
Loc: North America
I'm only 17 years old, but I know more than most people about electricity and what is right and what is wrong.

My father bought the house we are currently living in last August. It was built in about 1994. We are in Nova Scotia, Canada.

There is a separate detached garage, 24' by 36', with a subpanel.

The cable going from the main service in the basement to the exterior wall has this on the side:

1995 ALCATEL CANADA WIRE #2 AWG/3 ALUM ACM CSA NMD90 XLPE CANADEX 300V FT1

On the exterior is a non-metallic conduit. About 2 inches above grade, the conduit stops and the cable continues underground. Is this cable listed for direct burial?

My father is convinced it's okay since a building inspector passed it when we moved in... I doubt he paid tons of attention to the electrical.

Don't get me wrong, it's a beautiful house, but it's the same house with Romex run to where a shed once was, exterior fixtures lacking boxes and BX run to a lamp post.

It worries me and I need to know if it is okay or not.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102108 - 02/12/05 03:15 PM Re: Can you settle a dispute?
CRM Offline
Member

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
The keywords are NMD90, which is loomex. Table 19 of the CEC lists this cable for exposed wiring in dry or damp locations only. It is not approved for direct burial.

Top
#102109 - 02/12/05 04:36 PM Re: Can you settle a dispute?
jdadamo Offline
Member

Registered: 11/10/04
Posts: 37
Loc: Calgary, AB, Canada
Direct burial wire will say NMW or NMWU (Non-Metallic Wet) on it. That one is NMD (Non-Metallic Dry).

So you are correct.