The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102107 - 02/12/05 01:34 PM Can you settle a dispute?
Charles Offline

Registered: 10/09/03
Posts: 60
Loc: North America
I'm only 17 years old, but I know more than most people about electricity and what is right and what is wrong.

My father bought the house we are currently living in last August. It was built in about 1994. We are in Nova Scotia, Canada.

There is a separate detached garage, 24' by 36', with a subpanel.

The cable going from the main service in the basement to the exterior wall has this on the side:


On the exterior is a non-metallic conduit. About 2 inches above grade, the conduit stops and the cable continues underground. Is this cable listed for direct burial?

My father is convinced it's okay since a building inspector passed it when we moved in... I doubt he paid tons of attention to the electrical.

Don't get me wrong, it's a beautiful house, but it's the same house with Romex run to where a shed once was, exterior fixtures lacking boxes and BX run to a lamp post.

It worries me and I need to know if it is okay or not.

2014 / 2011 NEC & Related Books and Study Guides
#102108 - 02/12/05 03:15 PM Re: Can you settle a dispute?
CRM Offline

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
The keywords are NMD90, which is loomex. Table 19 of the CEC lists this cable for exposed wiring in dry or damp locations only. It is not approved for direct burial.

#102109 - 02/12/05 04:36 PM Re: Can you settle a dispute?
jdadamo Offline

Registered: 11/10/04
Posts: 37
Loc: Calgary, AB, Canada
Direct burial wire will say NMW or NMWU (Non-Metallic Wet) on it. That one is NMD (Non-Metallic Dry).

So you are correct.