#102074 - 12/09/04 11:03 AM sevice entrance
GETELECTRIC Offline
Member
Registered: 10/22/03
Posts: 172
Loc: toronto canada
I,m changing an old industriul unit into three lofts.I,m using the existing incoming 600v fusible disconnect which feeds a 225kva transformer which then feeds a 800amp metering section.My question is do I need a disco in between the transformer and metering board or does the 600v main disco cover this.
Top
Tools for Electricians:
#102075 - 12/09/04 12:11 PM Re: sevice entrance
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
The main disconnect should be fine until you get to the 800-amp 208-volt splitter.

Then you will have to install disconnect switches for each separate service, with or without utility or check meters, for the different lofts.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority
Top
#102076 - 12/10/04 05:29 AM Re: sevice entrance
GETELECTRIC Offline
Member
Registered: 10/22/03
Posts: 172
Loc: toronto canada
Thanks Tony thats what I thought.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals