The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102069 - 12/08/04 06:38 PM Identified conductor as common conductor between 3-way switches
foggy Offline
Junior Member

Registered: 10/21/04
Posts: 6
I know when wiring a 3-way light, a 3-conductor loomex will run between the 2 3-way switches' box, and normally the black one will be chosen as common, and the white and the red ones as travellers. The question is, can I use the white as common, the other two as travellers? I checked the code, but could not find the answer.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102070 - 12/09/04 12:00 PM Re: Identified conductor as common conductor between 3-way switches
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
4-034 * Three Way Switch Wiring

In some instances, it has been brought to our attention that the grounded circuit conductor is being switched in some three way lighting arrangements that are currently being installed. This is contrary to OESC 4-034, and 14-016 and in the interest of consistency will not be accepted.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

Top
#102071 - 12/10/04 06:40 PM Re: Identified conductor as common conductor between 3-way switches
foggy Offline
Junior Member

Registered: 10/21/04
Posts: 6
Thank you, Tony. CEC4-034(2) says it's not necessary to render the identified conductor if the connections are made so that an unidentified conductor is the return conductor from the switch to the outlet. I made a simple drawing in which I think the circuit is not against the rule. http://www.geocities.com/halosome/fauto/3way.JPG

Top
#102072 - 12/24/04 09:32 AM Re: Identified conductor as common conductor between 3-way switches
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Tony,

I don't think you misunderstood foggy's question.

Foggy is asking about the color coding of the wires, specifically using a white wire re-identified for use as an ungrounded switched conductor in a three way switching circuit.

The quote that you posted speaks to illegal three way switch circuits where the grounded conductor was switched. The simplest example would be one where you have two switches at two locations, each with a supply grounded and ungrounded conductor and a switched conductor feeding the lamp. Both supply leads are connected to the _traveller_ terminals, and then a conductor run from the _common_ terminal to the light fixture. With two switches you have two conductors, and depending upon switch position either conductor could be grounded or ungrounded. If both conductors are grounded, the lamp is off. If one is grounded and the other ungrounded, then the lamp is on. If both are ungrounded, then the lamp is off again, but electrically live.

-Jon

Top
#102073 - 12/29/04 10:16 AM Re: Identified conductor as common conductor between 3-way switches
DYNAMITE Offline
Member

Registered: 12/22/03
Posts: 37
Loc: Winkler, MB, Canada
4-034 subrule 2 return conductor to outlet or light can not be identified (white)