The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102051 - 11/06/04 03:48 PM Three-way switches for bathroom exhaust fans
Clyde Offline
Member

Registered: 10/17/03
Posts: 31
Loc: Leamington
I was asked a question the other day that applied when I was apprenticing but I havn't seen it lately.

There was a time (maybe still is) when it was reqired to have the bathroom exhaust fan on the three way switch. One switch outside and the other inside the washroom.

I do very little residential and am unsure as to weather this rule still applies. If it does, can someone tell me where this rule came from and what its intent was. I remember asking one of my teachers who just danced around the question. I concluded at the time that he didn't actully know.

If anyone can enlighten me, I would be appreciative.

Clyde

Top
2014 / 2011 NEC & Related Books and Study Guides
#102052 - 11/07/04 04:10 PM Re: Three-way switches for bathroom exhaust fans
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Never heard of that before. The only reason you would use a three way switch for an exhaust fan for a bathroom is if you had two bathrooms and they are exhausted by the same fan. Regular bathroom fan you only need one switch. Outside or inside it doesn't matter. I perfer inside.

Top
#102053 - 11/08/04 03:52 PM Re: Three-way switches for bathroom exhaust fans
Sandro Offline
Member

Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
This is still common practice. A better method that we use is two single pole switches wired in such a way that if either of the two switches is turned on, the fan would run.

The one switch would be located obviously in the bathroom, the second switch would need to be located at or near the wall thermostat.

This is a building code requirement, not a ESA or code book requirement.

The reason : Today's new homes are built more air tight then ever before. Because of this, building code requires some sort of "air exchanger" in each premises. More often than not, the bath fan controlled by these switches will be larger (90 or more cfm) compared to the other bath fans on the premises which are usually 50-60cfm. The large fan will most likely be located in the central or biggest bathroom of the residence.

If the home owner decides to get a proper Air Exchange unit (HRV), then the double switch requirement is exempt in the Ontario Building Code.

My 2 cents, I think this is just a band-aid solution to having a proper air exchanger in a house. I haven't met a single homeowner who regularly uses this method. If anything, I get numerous calls from homeowners asking me what this switch is by their thermostat and what it controls.

Hope this helps!

Sandro. www.santinoelectric.com

Top
#102054 - 11/09/04 10:05 AM Re: Three-way switches for bathroom exhaust fans
Whitey Offline
Junior Member

Registered: 10/01/03
Posts: 4
Loc: South Baptiste,Alberta,Canada
In Alberta, the Alberta Building code section 9.32.3.4 requires that the principle exhaust fan, be it the bathroom fan or say a hallway exhaust fan,which ever basically is the largest CFM unit is to be interconnected in a way that the activation of this fan automatically activates a supply fan or furnace fan on hot air heating systems,the supply fan must introduce air in quantitys equal to the air exhausted.

Top
#102055 - 11/12/04 02:51 PM Re: Three-way switches for bathroom exhaust fans
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Ontario Building Code Requirement

9.32.3.4. Principal Exhaust

(2) Except as permitted in Sentence (3), the principal exhaust fan shall be controlled by a manual switch.

(3) A principal exhaust fan required under this Articlem may be controlled by a dehumidistat or other automatic control
device where the manual switch required in Sentence (2) is capable of activating the fan regardless of the setting of the
automatic control.

(4) The switches required in Sentences (2) and (3) shall be centrally located in the dwelling unit and shall be identified
with the words VENTILATION FAN.

(5) The principal exhaust required in this Article may be provided by means of a heat recovery ventilator installed in accordance with Article 9.32.3.11.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority