The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 71 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102040 - 10/17/04 07:43 AM Marrettes in Panel
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Is there any code rule that says that you can not use marrettes in panels? You know if the wire is too short. CEC 6-212(1) talks about conductors feeding through. I never use marrettes in panels because I make sure the wires are long enough but I am curious if there is a code rule not allowing this.

Top
2017 / 2014 NEC & Related Books and Study Guides
#102041 - 10/19/04 08:35 PM Re: Marrettes in Panel
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
The code rule escapes me right now but yes for branch panels as long as cross sectional area does not exceed 40% or something like that.Marretts in control panels are not.Ive had inspectors offer to accept marretts as a solution where someone has landed more than one wire on breakers listed for only one wire.

Top
#102042 - 10/20/04 08:04 AM Re: Marrettes in Panel
aspencade Offline
Member

Registered: 10/19/04
Posts: 13
Loc: BC Canada
Robbie:

I think you got the rule already. The same rule specifies that you cannot use the panel as a junction box. If you make a connection with a marrette then you are using it as a junction box.

Don

Top
#102043 - 10/20/04 09:04 PM Re: Marrettes in Panel
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
See rule 12-3034 (ii).Wiring Space in Enclosures.
It is allowed except it's 75% cross sectional area not 40%.A circuit that enters and exits an enclosure in one or more directons is the defenition of a j-box. 6-212(1)keeps separately derived systems seperate or that's how CCS inspectors rationalize it.

[This message has been edited by frank (edited 10-21-2004).]