The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102040 - 10/17/04 07:43 AM Marrettes in Panel
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Is there any code rule that says that you can not use marrettes in panels? You know if the wire is too short. CEC 6-212(1) talks about conductors feeding through. I never use marrettes in panels because I make sure the wires are long enough but I am curious if there is a code rule not allowing this.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102041 - 10/19/04 08:35 PM Re: Marrettes in Panel
frank Offline
Member

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
The code rule escapes me right now but yes for branch panels as long as cross sectional area does not exceed 40% or something like that.Marretts in control panels are not.Ive had inspectors offer to accept marretts as a solution where someone has landed more than one wire on breakers listed for only one wire.

Top
#102042 - 10/20/04 08:04 AM Re: Marrettes in Panel
aspencade Offline
Member

Registered: 10/19/04
Posts: 13
Loc: BC Canada
Robbie:

I think you got the rule already. The same rule specifies that you cannot use the panel as a junction box. If you make a connection with a marrette then you are using it as a junction box.

Don

Top
#102043 - 10/20/04 09:04 PM Re: Marrettes in Panel
frank Offline
Member

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
See rule 12-3034 (ii).Wiring Space in Enclosures.
It is allowed except it's 75% cross sectional area not 40%.A circuit that enters and exits an enclosure in one or more directons is the defenition of a j-box. 6-212(1)keeps separately derived systems seperate or that's how CCS inspectors rationalize it.