The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (geoff in UK), 202 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101983 - 05/18/04 08:28 AM Cable protection
swooj Offline
Junior Member

Registered: 05/18/04
Posts: 1
Loc: Calgary,Alberta canada
I want to hook up two 120 V rectifiers in diffrent enclosures but I want to run one 4 conductor teck cable instead of 2 2conducotors cables and run a nipple between the two.Bring the teck cable to one rectifier and run the other conductors through the nipple to the other rectifier.One person tells me that I have to put the rectifiers on a double pole breaker because they are in the same cable instead of a single pole breaker for each individual rectifier.

Top
2014 / 2011 NEC & Related Books and Study Guides
#101984 - 05/18/04 03:54 PM Re: Cable protection
crash Offline
Member

Registered: 10/21/03
Posts: 130
Loc: Calgary Canada
The rule for this is 14-010,(b). If I'm reading the rule correctly, you should be okay with two seperate circuit breakers, as it appears you have two seperate circuits. If you were feeding the equipment with a 3 conductor teck cable (a 120/208V 3-wire circuit), I believe you would need a 2-pole breaker.

Top
#101985 - 05/21/04 07:48 PM Re: Cable protection
granam Offline
Member

Registered: 11/30/01
Posts: 21
Loc: Fort McMurray, Alberta, Canada
Is the termination enclosure of the first rectifier approved as a raceway? If not you won't be able to use it the way you're planning.