#101950 - 03/23/04 01:48 PM Code question reguarding box fill.
tippy9988 Offline
Junior Member
Registered: 02/10/04
Posts: 2
Loc: brighton ontario canada
Can someone please put OEC rule #12-3036(3) in to english for me? It all makes sence about the part where the useable space shall be reduced by that of the device, but the confusing part is just after that. Where are they coming up with these numbers? 82cm3??? the example did nothing to clear up the rule for me..... I just want to know what boxes to use when installing GFCI's. in an industrial atmosphere, ie. FS boxes 1110 ...
Top
Tools for Electricians:
#101951 - 03/23/04 04:11 PM Re: Code question reguarding box fill.
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Required space for conductors:
a) 1.5 cubic inches per 14 AWG
b) 2 cubic inches per 12 AWG

For a device over one inch deep, deduct from the actual volume of the box: 5 cubic inches per inch of depth of the device. (for a 1.5 inch deep device, deduct 7.5 cubic inches)

That rule is a good example of poor workmanship. If the drafter of that rule worked for me, I would fire him.

tim
Top
#101952 - 03/23/04 08:55 PM Re: Code question reguarding box fill.
crash Offline
Member
Registered: 10/21/03
Posts: 147
Loc: Calgary Canada
Fire him. Send him back to junior high. And take his metric conversion calculator away! Then hand him a tape measure and tell him to find the 1/100cm marks on it.

[This message has been edited by crash (edited 03-23-2004).]
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 40 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals