#10195 - 06/01/02 08:34 AM Push-ups or Jumping Jacks?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I've noticed that many of the "Home Inspection Reports" related to real-estate transactions recommend "exercising" circuit breakers on a regular basis.
What are your thoughts?


Work Gear for Electricians and the Trades

#10196 - 06/01/02 09:03 AM Re: Push-ups or Jumping Jacks?  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Redsy,

I've always thought the same thing and would probably bet that I've read it somewhere in mfgrs instructions or recommendations. I've seen a lot of times where someone will turn off their Main to do work (as recommended) and it will not reset, and I was thinking that 20+ years in one position in a damp basement can't be good for anything. [Linked Image]

Bill


#10197 - 06/01/02 10:01 AM Re: Push-ups or Jumping Jacks?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
I had heard some years ago of a UL requirement to 'mechanically' operate breakers manually but have never verified this.


#10198 - 06/01/02 10:29 AM Re: Push-ups or Jumping Jacks?  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I think it's a good idea to cycle breakers, maybe off and on a couple of times ar least once a year.


#10199 - 06/01/02 12:38 PM Re: Push-ups or Jumping Jacks?  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
That just happened to me last week. I swung by a friends to demo a floor box she didn't want before the new carpet was put down the next day. I figured I could squeeze it in before my final at school the same night. Rather that trace out which circuit I threw the main. On my way out I turned it back on and wouldn't you know it, the thing would not reset. I don't know if it was from not being exercised or if it just broke. It did not sound to good inside.


#10200 - 06/01/02 02:58 PM Re: Push-ups or Jumping Jacks?  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,232
West Virginia
Outdoor discos mounted below OH meter bases are the worst... Especially when SEU cable and a "WP" hub is involved. I tend to shy away from switching any mains unless absolutely neccesary.

*crunch*


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#10201 - 06/01/02 10:03 PM Re: Push-ups or Jumping Jacks?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
66vdub-- sounds like a classic high-pucker-factor 'trap.'

Rambling Notes on circuit breakers after installation

NETA MTS-2001 7.6.1.1 Circuit Breaker INSPECTION PROCEDURES “Inspect ∙ Clean ∙ Operate the circuit breaker to insure smooth operation…”

{Factory-applied lubricants harden/leach. Do not use spray lube/cleaner unless it’s in CB maintenance instructions.}

Vaguely related links: http://www.nema.org/products/div5/5ab/guess.html http://www.seekandsource.com/news/Articlespec.Asp?Article_id=ARTI93 http://www.powellservice.com/PASD%20Test%20Procedures/TABLE%2010.7.doc http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000291.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000253.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000607.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000615.pdf http://standards.ieee.org/colorbooks/sampler/Bluebook.pdf


[This message has been edited by Bjarney (edited 06-02-2002).]


#10202 - 06/02/02 12:00 AM Re: Push-ups or Jumping Jacks?  
hurk27  Offline
Member
Joined: May 2002
Posts: 68
Portage, Indiana
does any body use nolox when you install a main or any other high amperage breaker on a buss that's aluminum. I have had many breakers fail because of this problem and have been using the nolox for some time.
:Wayne


Be Fair, Be Safe
Just don't be Fairly Safe

#10203 - 06/02/02 02:55 PM Re: Push-ups or Jumping Jacks?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
hurk— Be Careful. That may be a misapplication if using particle-bearing inhibitor or any substance on the spring-clip/stab end of molded-case breakers. Conductive particles in sticky paste may incite carbon tracking and breakdown if left in contact with {bakelite} insulating surfaces.


[This message has been edited by Bjarney (edited 06-03-2002).]


#10204 - 06/03/02 07:01 AM Re: Push-ups or Jumping Jacks?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I've wiped a little nolox on meter stabs when I've had difficulty removing the meter.


Page 1 of 2 1 2

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8164 MB (Peak: 0.9933 MB) Zlib enabled. Server Time: 2017-03-23 23:57:35 UTC