The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (hyetal), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101914 - 02/09/04 07:07 AM Ground and Disconnect at Detached building
sparkyky Offline
Junior Member

Registered: 02/08/04
Posts: 3
Loc: lower 48
Greetings ~

Can you inform me of the CEC residential requirements for any grounding electrode,and type needed ,in addition to the feeder ground conductor, at the detached structure,when a feeder is installed from the building where the primary service is located?

I also would like to know where this residential feeder disconnect is required to be located at this detached building.

Many Thanks

2014 / 2011 NEC & Related Books and Study Guides
#101915 - 02/09/04 05:36 PM Re: Ground and Disconnect at Detached building
Tony Moscioni Offline

Registered: 05/15/01
Posts: 144

Two or More Buildings


Ground system neutral at main service;

Ground neutral at second building to an electrode (no bond wire) or:

Run a separate neutral and bond wire to second building (not for buildings housing livestock)

Main disconnecting means required at second building in all installations at point of entry, adjacent to distribution equipment.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#101916 - 02/10/04 04:06 AM Re: Ground and Disconnect at Detached building
sparkyky Offline
Junior Member

Registered: 02/08/04
Posts: 3
Loc: lower 48
thank you,Tony M

The NtlElecCode NEC for USA requires a grounding electrode in all detached buildings where there is a sub feeder ran.

The CEC then,does not ,as it depends soley on the ground wire ran with the feeder?