Jacket As A Barrier For Cables In A Cable Tray

Our code and SPE 1000 require “conductors” to be insulated for the same voltage if inside the same raceway.

One way of doing this for “jacketed cables” is to have an interpretation that the jacket is an effective barrier and we do not need additional physical separation or equal voltage insulation.

This is covered in rule 16-212 (d) for class 2 circuits. For Class 1 circuits rule 12-904 (2) (b) applies if the jacket is 1.5 mm thick, or (c) applies if they are for supply or control of remote devices and are insulated for the highest voltage.

Therefore if you have jacketed cables, you do not need to separate the cables in a cable tray.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority
Top
Tools for Electricians:

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals