The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
39 minutes 29 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
1 registered (LongRunner), 98 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101795 - 05/07/03 11:10 AM Running pipe in a dwelling.
Nicholas Offline
Junior Member

Registered: 05/05/03
Posts: 2
Loc: St. Cath. On
If a customer wants his home ran in pipe rather than NMD, what rules should I be aware of? Can I use shared neutrals as long as the continuity of the neutral is independant of the device connections?
Also do I have to de-rate using table-5C
although these circuits are already de-rated to 80%?

Top
2014 / 2011 NEC & Related Books and Study Guides
#101796 - 05/07/03 02:24 PM Re: Running pipe in a dwelling.
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
You can use shared neutrals, providing -
1. the two hot wires sharing a neutral are supplied from different panel busses, and
2. all the outlets supplied from those two circuits use the same neutral, if there is more than one neutral in the conduit.

You say "these circuits are already de-rated to 80%" Is this the "continuous load" derating, for Rule 8-104? If so, you only need to derate for that or Table 5C, whichever results in the largest wire size. 8-104(6)