The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101792 - 04/25/03 07:34 PM Neutral Service Conductors
ThorahSparky Offline
Junior Member

Registered: 04/13/03
Posts: 13
Loc: Orillia,ON,Canada
I'm curious to know what the requirement in Ontario and Canada is on the use of a reduced sized neutral conductor on Residental Services. My interpretation of Rule 4-022 (1)+(2) is that it is permitted and it also could be uninsulated as well. Realistically very little current goes through the neutral as most large loads in a house are already balanced (240V) and the 120V loads are somewhat small in comparision. Is this method acutally permitted and is it used?

Top
2014 / 2011 NEC & Related Books and Study Guides
#101793 - 04/27/03 01:06 PM Re: Neutral Service Conductors
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Rationale for Rule 4-022.

The neutral conductor of a system is a current-carrying conductor and shall be sized to carry the unbalanced load of the system. In case of a service neutral, the conductor shall also be capable of carrying fault current, and therefore the ampacity of the service neutral is bound by the Rules for sizing the system ground as well as the General Rules for neutral conductors.

Intent for Rule 4-022.

Fundamentally, we intend that the neutral conductor have sufficient ampacity to carry the unbalanced load. A demand factor of 70% may be applied to that portion of the unbalanced load in excess of 200 A, but no easement should be allowed in the ampacity of the neutral conductor for any portion of the load that consists of electric discharge lighting.

Although the CE Code, Part I, does not specifically mention harmonics, harmonics can cause heating in the neutral conductor. Harmonics caused by certain types of non-linear loads (eg, personal computers, printers, variable speed motor drives, certain types of electric discharge lighting) should be taken into consideration when sizing a neutral conductor. The use of 2-wire rather that 3-wire branch circuits is a good example of dealing with neutral problems in branch circuits.

Furthermore, we intend that the service neutral conductor not be smaller than No. 10 AWG copper or No. 8 AWG aluminum and the ampacity be not less than the ampacity of the grounding conductor that is sized by Rule 10-812.


When a bare neutral conductor is run in a raceway with insulated conductors, we intend that the ampacity of the neutral conductor be based on the insulation temperature rating of the adjacent circuit conductors. For example, if the circuit conductors were No. 6 AWG Cu type TW that is rated at 60°C, then the ampacity of the neutral would be based on Column 2 of Table 2, which would be 55 amperes. If the circuit conductors were type RW90 XLPE, then the ampacity of the neutral would be 65 amperes, based on Column 4 of Table 2.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals