#101762 - 02/27/03 01:02 PM Supplementary Protectors
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
Supplementary Protectors

(Sometimes called Mini-Circuit Breakers)

In December 1998, a maintenance worker received second
degree burns while resetting a “Supplementary Protector” that
was located within a Control panel. Investigation revealed that
the Supplementary Protector was reset while the equipment was still energized and fault condition was on the equipment protected by the Supplementary Protector.

It is important to note that each piece of electrical equipment has it’s own place and function within a circuit.

Circuit Breakers are Certified to Standard CSA 22.2 #5.1 and
Supplementary Protectors are Certified to Standard CSA 22.2
#235.


By Definition:

Circuit breaker

A circuit breaker is a device designed to open and close a circuit by non-automatic means; and to open a circuit
automatically on a predetermined overcurrent without injury to itself when properly applied within its ratings. Circuit breakers
are intended for the protection of services feeders, and branch circuits in accordance with the Canadian Electrical Code, Part I.


Supplementary protector

A supplementary protector is a device designed to open a circuit automatically on predetermined value(s) of time versus
current or voltage within an appliance or other electrical equipment. Supplementary protectors are intended for use as a
component within an appliance or other electrical equipment where branch circuit overcurrent protection is already provided
(or is not required) in accordance with the Rules of the Canadian Electrical Code, Part I. Supplementary protectors shall not be
used for branch circuit protection.


Since 1994 The Ontario Electrical Safety Code requires:

Under Section 14-012, Ratings of Protective and Control
Equipment…

a) “Electrical equipment required to interrupt fault currents
shall have ratings sufficient for the voltage employed and for the
fault current that is available at the terminals.”

The Difference?
Circuit Breakers and Fuses are “required” to be able to interrupt fault currents,
Supplementary Protectors are not.

It is important to realize that, unlike Circuit Breakers, all Supplementary Protectors certified to C22.2 No. 235, have no code application for branch overcurrent circuit protection.

This means that the Supplementary Protectors may rely on the fuses or circuit breakers ahead of them in the circuit for
overcurrent (Short Circuit) protection.
Closing them into a fault is subjecting them to a situation for which they were not
designed or certified to do. The consequences of this misapplication can be devastating.


The difficulty is in identifying whether the device is a “Circuit
Breaker” or a “Supplementary Protector”.

It is also difficult to check, since there is no marking to identify the difference between “real” circuit breakers and
supplementary protectors. This makes it very difficult to identify a device built to the supplementary specification versus a device
built to the circuit breaker specifications.

We have recently asked the certification organizations to look into marking the devices so they can be differentiated.

In some cases, the only way to tell is to look up the product code number in the manufacture’s catalogue. To
complicate the matter further, some literature refers to the
Supplementary Protectors as circuit breakers, until you look closer.

Some clues to a Supplementary Protectors are that they tend to be located with-in equipment, DIN rail mounted, and usually are
physically smaller than circuit breakers, but not always.

Note that Rule 2-304 (1) OESC states that ….

“No repairs or alterations shall be carried out on any live
equipment.”

This means that, as with any equipment, internal components
should not be reset or adjusted with the power on.

Electrical Inspection suggests the following:

• all such equipment should have warning signs indicating that
the equipment’s main disconnect be opened before any
devices within are reset, and;

• any personnel likely to be working on such equipment be
advised of this concern and the proper procedure for
resetting these devices.

Disconnecting power, in accordance with the Code, ensures that
workers can safely reset supplementary protectors without fear of
failure

In Summary:

• Never work within equipment that is energized. Turn off
the Main disconnect feeding the equipment, before
entering an equipment enclosure.

• Use Safe Lockout, Tag Procedures.

• Use Warning Signs
Top
Tools for Electricians:

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 90 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals