The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 184 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101758 - 02/26/03 01:40 PM Voltage Drop Question
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
I have a question about voltage drop. I know how to use D3 Table, I can figure out the voltage drop for a two wire circuit No-problem. I don't know how to figure out the voltage drop for a three phase circuit though. In the old code books it was easy because on Table D5 they used to give you the -CM Area- in the 2002 code book they don't. The old formula: CM=(K)(I)(L)(1.73)
---------------
VD

Table D5 has taken away the CM Area.
So how do you find the voltage drop in a three phase circuit using the 2002 CEC?
For example three-phase (no neutral) going to a motor controller.
Sorry for all the questions but I thought that I would take advantage of all the expertise.

Top
2014 / 2011 NEC & Related Books and Study Guides
#101759 - 02/27/03 03:57 PM Re: Voltage Drop Question
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Hey is anybody out there? Hey Tony could you help me with my question?

Thanks

All that I am looking for is if I was to use the 2002 CEC only would I be able to find the voltage drop in the three phase circuit. I don't think I can. I think that I would require some other book most likely a manufacturers pamplet with info on the specific wire. I'm not sure though maybe I'm not looking in the right place in the code book that's why I asking the question. I am positive that people have calculated voltage drops in three phase circuits before. I am just curious on how they do it with just the code book.
Thanks

Top
#101760 - 02/27/03 04:33 PM Re: Voltage Drop Question
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Robbie,

Here is the formula in calculating Voltage Drops in Three Phase Circuits:


Three Phase Formulas as Follows:

%VD,3PH= KFactorxAmpsxLength of CCT in Metres
Phase to Phase Supply Voltage-volts


Single Phase Formulas as Follows:

%VD,1PH= KFactorx1.15xAmpsxLength in Metres
Phase to Neutral Supply Voltage

If you are using the OESC 2002'look under Table D3.

For other nominal voltages, multiply the distances in metres by the other nominal voltage (in volts) and divide by 120.


Example on use of Table:

Consider a two conductor circuit of No. 12 AWG copper NMD90 carrying 16 A at nominal 240 V under maximum ambient of 30°C. The maximum run distance from the centre of distribution to the load without exceeding a 3% voltage drop is:

Maximum run length for No. 12 AWG, 16 A, 1% voltage drop at nominal 120 V from Table is: 6.1 m

Distance Correction Factor to be used is:

From Table 2, allowable ampacity for 2
conductor No. 12 AWG NMD90 (90°C rating per Table 19) is 20 A. The given current is 16 A or 80% of the allowable ampacity.

The Distance Correction Factor to be used, from Note (3), 90°C row, 80% column, is 1.00.


The maximum run length is:

6.1 m x 3% x 1.00 x 240v = 37m
120v

Beyond this distance a larger size of conductor is required, ie, No. 10 AWG (30 A allowable ampacity) beyond 37 m up to and including 62 m.

9.7 ,m x 3% x 1.06 x 240v = 62m
120

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

Top
#101761 - 02/27/03 04:40 PM Re: Voltage Drop Question
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Thanks Tony, Is it possible to calculate the voltage drop of a three phase circuit using only the 2002 CEC?

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals