#101733 - 02/07/03 01:24 PM Patient Care Receptacles: How many are required?
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
Patient Care Receptacles: How many are required?


Question:
What number of duplex receptacles and branch circuits are required per patient care location?

Answer:
You might want to read the Z32-99 "Electrical Safety and Essential Electrical Systems in Health Care Facilities Standard...it states in Table #6 the following info:

Basic Care Areas= 1 duplex per patient care location & 0.5 number of branch circuits per patient care location.

Intermediate Care Areas= 3 duplex's per patient care location & 1.5 number of branch circuits.

Critical Care Areas= 8 duplex's per patient care location & 4 number of branch circuits.

Operating Rooms= 14 total (6 on walls & 8 on ceiling) & 7 number of branch circuits.

0.5 means one circuit shared with one other bed location.

1.5 means one dedicated circuit plus one circuit shared with one other bed location.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority
Top
Tools for Electricians:

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals