The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Trumpy
01/20/17 06:20 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 17
Trumpy 15
gfretwell 15
Who's Online
1 registered (Admin), 10 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101715 - 12/29/02 01:24 AM nonmetallic sheathed cable
sparkyga Offline
Member

Registered: 04/01/02
Posts: 15
Loc: V.K.
Hi Guys

I have never seen loomex(NMD) surface mounted in a house(without a raceway), but according to the code unless it is exposed to mechanical damage or closer then 1.5 Metres from the floor it is allowed (CEC 12-518). I had a discussion with an individual and he is saying there is no problem with this if he wanted to do it. This leaves allot of room for bad judgement. I have never seen a house wired in this matter and it obviously would not look good but can you prove to me that it can not be done. If he decided to surface mount a cable from a switch to a light in the ceiling and not use a raceway could he get away with it

Thanks
Greg

Top
2017 / 2014 NEC & Related Books and Study Guides
#101716 - 12/30/02 11:42 AM Re: nonmetallic sheathed cable
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Greg,

I don't like the answer, but quite frankly, he could actually pass inspection.

The code only specifies mechanical protection if it was installed less than 1.5m.

As well, there is no requirement in the standard CAN/CSA-C22.2 No. 48-M90
(Reaffirmed 2000)
Nonmetallic Sheathed Cable.


Rationale and Intent for Rule 12-518.

Where cables pass through floors or are located less than 1.5 m above a floor, we intend that they be protected from mechanical damage such as by the use of metal conduit or guard strips or installed in a location where there is no potential hazard.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

Top
#101717 - 12/31/02 02:08 PM Re: nonmetallic sheathed cable
ZackDitner Offline
Member

Registered: 10/11/02
Posts: 46
Loc: Kitchener, Ontario, Canada
so if i wired my whole house with NM cable 5' off the floor nailed to the walls there would be no problem?

Top
#101718 - 01/02/03 04:36 PM Re: nonmetallic sheathed cable
sparkyga Offline
Member

Registered: 04/01/02
Posts: 15
Loc: V.K.
Thanks for the answer:

It is good to know this just in case I run into a situation where I forget to pull the electrical in the walls before the drywall.This way I can just hang it from the ceilings and walls unless I have a few monkeys that might cause mechanical damage by hanging on it.!!!!!!

Later