#101703 - 12/11/02 12:42 PM GFCI Protection Required for Kitchen Counter Receptacles
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
Notice

Effective January 1, 2003 GFCI Protection will be Required for
Kitchen Counter Receptacles

The 2002 edition of the Ontario Electrical Safety Code includes an Ontario amendment to Rule 26-700,
which requires Ground Fault Circuit Interrupter (GFCI) protection for Kitchen Counter receptacles
effective January 1, 2003.

The new Subrule (26-700(12) states that effective January 2003:

(12) Receptacles located in kitchens and installed within 1 m of a kitchen sink along the wall
behind counter work surfaces shall be protected by a ground fault circuit interrupter of the Class A
type.

Appendix B note: Distance of 1 m is measured from edge of kitchen sink.

The following guidelines shall be used for consistent interpretation and application of this new subrule
effective January 1, 2003.

1. This rule applies to all receptacle installations located within 1 m of a kitchen sink along the wall behind
counter work surfaces where the plans or application for inspection is received on or after January 1, 2003

2. This rule applies to all kitchens.

2.1. Kitchen is defined as “a place (as a room) with cooking facilities”

2.2. A cooking facility is defined as a range or stove (electric or gas supply) for cooking. Hot plates,
microwaves, etc are not defined as a cooking facility for application of this rule.

3. In dwelling units, Rules 26-712(d) and 26-722(b) require that kitchen counter receptacles be split
receptacles connected to multi-wire 15 amp branch circuits. Rule 26 -726 permits the installation of 5-20
RA (T-slot) receptacles connected to single 20 amp branch circuits as an alternative to split receptacles and
circuits. In both cases adjacent receptacles shall not be connected to the same branch circuit.

Receptacles that are located on either side of a kitchen sink shall not be considered as adjacent for the
application of this requirement and can be connected to the same branch circuit when applying this new
rule.

If you have any questions regarding this directive, please contact your local Technical Advisor (whose
name and number is listed in your bulletins).

Tony Moscioni
Electrical Inspector
Electrical Safety Authority
© Electrical Safety Authority - 2002
Top
Tools for Electricians:
#101704 - 12/11/02 06:38 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
ZackDitner Offline
Member
Registered: 10/11/02
Posts: 46
Loc: Kitchener, Ontario, Canada
So we have to provide multiwire (split) GFCI recepticals within 1m of the sink??

Double pole GFCI's aren't cheap
Top
#101705 - 12/13/02 04:35 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
Sandro Offline
Member
Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
Zack..... read the code again...

'Rule 26 -726 permits the installation of 5-20 RA (T-slot) receptacles connected to single 20 amp branch circuits as an alternative to split receptacles and
circuits.'

Simply use a single 12-2 run and use a single 20amp GFCI breaker or plug and, as the code states, you only need ONE GFI as you can tandem the 20Amp feed and put a receptacle on either side of the sink.

[This message has been edited by Sandro (edited 12-13-2002).]
Top
#101706 - 12/14/02 01:30 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
SamC Offline
Member
Registered: 03/27/02
Posts: 15
Loc: Canada
You can also buy 20 amp T-slot GFCI
receptacles from Leviton. I believe they cost about $25

SamC
Top
#101707 - 12/17/02 02:29 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
ggardiner Offline
Member
Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
If this is the case for areas used for cooking does that mean you still run split receptacles around a counter in a refreshment area where no stove is present but microwaves and hot plates are?
Top
#101708 - 12/17/02 02:47 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1685
Loc: New York City
I didn't know you could get 125volt/20 amp "T-Slot" receptacles in Canada?

I always thought Canadian 5-20 sockets were designed to only accept 20-amp plugs, not 15?

At least that's the impression I got from a DIY book I have at home....(yes I know lots of those DIY books are mighty suspect )

Can someone set me straight on this?
Top
#101709 - 12/17/02 02:52 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
ggardiner Offline
Member
Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
Yes you can purchase T slot receptacles in Canada it is not common mainly because of the cost in comparision to the 15 amp receptacles.
Top
#101710 - 01/09/03 03:42 PM Re: GFCI Protection Required for Kitchen Counter Receptacles
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
What about a combination of 20 amp and split 15 amp. How do you figure how many of each?
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, HotLine1), 90 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals