The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 160 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101701 - 12/07/02 04:13 PM 10-208 for a car wash
bill woods Offline
Member

Registered: 11/21/01
Posts: 45
Tony I'm confused. I have a car dealership with a separate building for a car wash. The main distribution is in the dealership. The car wash is fed from a 400A breaker in the main distribution. Does the car wash get its own ground rods? Would you explain 10-208 to me please.

Top
2017 / 2014 NEC & Related Books and Study Guides
#101702 - 12/07/02 06:44 PM Re: 10-208 for a car wash
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
Bill, there are two options.

10-208 (a) is used when the wiring method between the buildings does not contain a bonding wire, such as triplex run overhead, and when there are no other metallic connections between the buildings (piping, other wiring systems, etc).

10-208 (b) is used when the wiring method between the buildings does contain a bonding wire, such as TECK cable or conduit, and when there are other metallic connections between the buildings. Method B cannot be used in buildings housing livestock.

The sketches below show typical single phase installations, but would apply to three phase systems also. They are for illustrative purposes only and not intended to represent actual installations.





Ed



[This message has been edited by electric-ed (edited 12-07-2002).]