The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 04:10 PM
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 165 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101701 - 12/07/02 04:13 PM 10-208 for a car wash
bill woods Offline

Registered: 11/21/01
Posts: 45
Tony I'm confused. I have a car dealership with a separate building for a car wash. The main distribution is in the dealership. The car wash is fed from a 400A breaker in the main distribution. Does the car wash get its own ground rods? Would you explain 10-208 to me please.

2014 / 2011 NEC & Related Books and Study Guides
#101702 - 12/07/02 06:44 PM Re: 10-208 for a car wash
electric-ed Offline

Registered: 07/08/02
Posts: 184
Loc: Canada
Bill, there are two options.

10-208 (a) is used when the wiring method between the buildings does not contain a bonding wire, such as triplex run overhead, and when there are no other metallic connections between the buildings (piping, other wiring systems, etc).

10-208 (b) is used when the wiring method between the buildings does contain a bonding wire, such as TECK cable or conduit, and when there are other metallic connections between the buildings. Method B cannot be used in buildings housing livestock.

The sketches below show typical single phase installations, but would apply to three phase systems also. They are for illustrative purposes only and not intended to represent actual installations.


[This message has been edited by electric-ed (edited 12-07-2002).]