The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 220 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101673 - 10/15/02 02:54 PM Dial Setting for Overload Protection
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
The trip values for motor overloads are as per OESC Rule #28-306 . . .

However, if you follow manufacturers instructions, you would be suprised to discover the following:

For Motors with a Service Factor of 1.15

Set the dial setting to the motor nameplate full load amperes.

Then the device trips at 125% of the full load amperes.

For Motors with a Service Factor of 1.00

Set the dial setting to only 90% of the motor nameplate full load amperes.

Then the device trips at 115% of the full load amperes.


Tony Moscioni
Electrical Inspector
Electrical Safety Authority

Top
2014 / 2011 NEC & Related Books and Study Guides
#101674 - 10/15/02 05:40 PM Re: Dial Setting for Overload Protection
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
- - - and for motor starters that require overload heaters to be installed in the field, the heater specified on the instructions are for motors with a Service Factor of 1.15.

For motors with a Service Factor of 1.00 you must install one heater size smaller in order to provide proper protection.