#101673 - 10/15/02 02:54 PM Dial Setting for Overload Protection
Tony Moscioni Offline
Moderator
Registered: 05/15/01
Posts: 144
Loc: CANADA
The trip values for motor overloads are as per OESC Rule #28-306 . . .

However, if you follow manufacturers instructions, you would be suprised to discover the following:

For Motors with a Service Factor of 1.15

Set the dial setting to the motor nameplate full load amperes.

Then the device trips at 125% of the full load amperes.

For Motors with a Service Factor of 1.00

Set the dial setting to only 90% of the motor nameplate full load amperes.

Then the device trips at 115% of the full load amperes.


Tony Moscioni
Electrical Inspector
Electrical Safety Authority
Top
Tools for Electricians:
#101674 - 10/15/02 05:40 PM Re: Dial Setting for Overload Protection
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
- - - and for motor starters that require overload heaters to be installed in the field, the heater specified on the instructions are for motors with a Service Factor of 1.15.

For motors with a Service Factor of 1.00 you must install one heater size smaller in order to provide proper protection.

Ed
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals