The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 08:52 AM
Would ELV branch circuits be a good idea?
by geoff in UK
Today at 03:25 AM
Why cables look like they do
by Trumpy
Today at 02:20 AM
Re: Fabricating Guards out of Lexan?
by Trumpy
Today at 12:36 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
Trumpy 12
Webmaster 12
ghost307 10
frank 9
Who's Online
1 registered (ghost307), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101662 - 09/06/02 05:21 AM 12-1502 * ENT with Thermal Insulation
Tony Moscioni Offline
Moderator

Registered: 05/15/01
Posts: 144
Loc: CANADA
Section 12

12-1502 * ENT with Thermal Insulation

Question:
Does 2002 Code Rule 12-1502 or 12-1508, restrict the use of ENT when blanketed with Thermal Insulation?

Answer: No!

Background:
1998 Code Rule 12-1502(c) did not permit ENT to be used where enclosed in thermal insulation, this restriction has been deleted in the 2002 Code.

Rationale:
CSA conducted tests on ENT enclosed in thermal insulation and based on the results concluded the raceway was capable of dissipating the heat generated by current flow in conductors with no adverse effect on the ENT or its conductors.

Top
2017 / 2014 NEC & Related Books and Study Guides
#101663 - 09/06/02 02:32 PM Re: 12-1502 * ENT with Thermal Insulation
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
ENT is limited to installation-
a. in masonry walls,
b. in concrete slabs,
c. where exposed, and
d. for direct earth burial, when approved.

There was no need for the restriction against enclosing it in thermal insulation, as none of the permitted uses involve insulation.

Maybe it is permitted in the space between two masonry walls, where insulation is often used.

Ed

Top