The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 293 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101606 - 02/13/02 04:45 PM Question about 600Y347
CTwireman Offline

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Do you use 600Y347 instead of 480Y277 in Canada, or are both voltages available?

What is the commonly used color-coding for a 600/347 volt system?

As you probably know allready we use brown-orange-yellow-gray for 480.

Any idea why 600 is not used in the U.S.?

2014 / 2011 NEC & Related Books and Study Guides
#101607 - 02/14/02 01:33 PM Re: Question about 600Y347
Tony Moscioni Offline

Registered: 05/15/01
Posts: 144
In Canada, the primary voltage for industrial / commercial secondary distribution is 347/600v.

However, you can also spec 277 / 480v if so desired.

The automotive industry and most of it's subsidaries use the 480 volt secondary distribution system.

Rule 4-036 Colour of Conductors

Where colour coded circuits are required, the following colour coding shall be used, except in the case of service-entrance cable and insofar as Rules 4-030, 4-032, and 6-308 may modify these requirements:

1 phase ac or dc (2-wire) — 1 black and 1 red
1 black and 1 white*† (where identified conductor is required);
1 phase ac or dc (3-wire) — 1 black, 1 red, and 1 white*†;
3 phase ac — 1 red (phase A),
1 black (phase B),
1 blue (phase C), and
1 white* (where neutral is required)
*Or natural grey;
†Or white with coloured stripe (see Subrule 4-034).
(4) Where the mid-point of one phase of a 4-wire delta-connected secondary is grounded to supply lighting and similar loads, the conductors shall be colour coded in accordance with Subrule (3) and the phase A conductor shall be the conductor having the higher voltage-to-ground.

Rationale for Rule 4-036.
It is desirable that there be a universal or at least a national colour code for conductors, rather than several varieties, to avoid confusion and provide greater safety.

Intent for Rule 4-036.
In Subrule (3), we intend that when colour-coded circuits are required, phase A conductors be coloured red, phase B conductors be coloured black, phase C conductors be coloured blue, and the neutral conductors be coloured white or white with a coloured stripe where more than one system is present in the raceway, box, or enclosure.
In Subrule (4), occasions arise where a delta-connection secondary is grounded to supply lighting and similar loads in addition to polyphase motors, so that the one phase has a higher voltage-to-ground than the other two phases. We intend that this phase be designated as Phase A and the conductors coloured red as per Subrule (3).

Tony Moscioni
Electrical Inspector
Electrical Safety Authority

#101608 - 02/14/02 04:20 PM Re: Question about 600Y347
CTwireman Offline

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Thanks for your answers.

The brown/orange/yellow/gray is not a code requirement here in the US, but it is commonly used and specified.

How do you differentiate between different voltage systems in a building, ie, a building with 600/347 and 120/208? If I interpret the CEC rule correctly, do different voltage systems utilize the same color code?

120/240 is also a common voltage system in Canada, right?

I am under the impression that US and Canadian systems are similar but there are also some big differences.

[This message has been edited by CTwireman (edited 02-14-2002).]

#101609 - 02/15/02 10:43 AM Re: Question about 600Y347
ggardiner Offline

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
Most of us use the brown yellow orange for 600 volt wiring.I'm not sure if this was changed in the 2002 code but I know it not a code but a trade practice.