#101505 - 04/22/01 12:49 PM Re: Grounding ... CEC vs NEC  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
From March issue of EBmag (ebmag.com)

"Both the Canadian Electrical Code (CEC) in Canada and the National Electrical Code (NEC) in the U.S. deal extensively with grounding and bonding issues and for the same reason – to minimize the possibilities of electrical fires and shocks. However, each code tackles the issues in a different way, in many aspects: terminology, materials and methods of installation. "

More:
http://www.ebmag.com/curr/article1.phtml?id=394

Any Comments?


Tools for Electricians:

#101506 - 04/26/01 09:43 PM Re: Re: Grounding ... CEC vs NEC  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
I notice the requirement in the CEC is for 10 Ft ground rods. Is there also a requirement for a second rod if certain resistance measurements cannot be proven? (Down here (US) We are supposed to be at 25 ohms or less.)


[Linked Image]
Bill


#101507 - 05/28/01 09:53 PM Re: Re: Grounding ... CEC vs NEC  
ElecTrainer  Offline
Member
Joined: Feb 2001
Posts: 20
South Porcupine,ON. CA.
Quote
Originally posted by Bill Addiss:
I notice the requirement in the CEC is for 10 Ft ground rods. Is there also a requirement for a second rod if certain resistance measurements cannot be proven? (Down here (US) We are supposed to be at 25 ohms or less.)


[Linked Image]
Bill


The CEC deals with this problem by design rather than state a specific resistance. For low voltage ie. less than 750 volts, as per section 10-500 "the bonding and grounding conductors will, without becoming damaged, carry the fault current efficiently enough to allow the prompt functioning of overcurrent devices and the voltage rise due to the fault will be limited to a safe level"
In other words fault currents are predicted for worst case conditions and the bonding/grounding system designed to suit.
High voltage ie. over 750 volts has a section (36) dedicated specially to controlling or guarding against dangerous fault conditions to protect equipment and personelle.
Grounding and bonding is a particularly critical subject and is dealt with at an engineering level to attain the best possible safety conditions. Every situation is different and requires due consideration.
ElectTrainer



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7512 MB (Peak: 0.8752 MB) Zlib enabled. Server Time: 2017-03-27 12:38:44 UTC