The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (Ruben Rocha), 174 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101463 - 03/22/07 05:55 PM uf cable near pool
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
As long as I stay at least 10 ft. away from the wall of the pool, can't I run uf cable to post lamps around the pool? Thanks Steve...

Top
2017 / 2014 NEC & Related Books and Study Guides
#101464 - 03/22/07 06:31 PM Re: uf cable near pool
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I say you only have to stay 5 feet away from the pool per 680.22(B). UF wire could be installed at least 12" deep and GFCI protected if you can satisfy 300.5 T.300.5 Column 4.
_________________________
George Little

Top
#101465 - 03/22/07 06:39 PM Re: uf cable near pool
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks George, I don't know where I got the 10ft. at.. Steve..