#101377 - 03/13/07 06:38 AM Smoke detectors in HVAC ducts
sudsy4 Offline
Member
Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
On the job I'm on, the smoke detectors in the HVAC ducts are powered from the convienience outlets in the RTU's. I don't have a copy of NFPA 72, but this doesn't seem like a good idea to me. Should any one trip or turn off a breaker for these outlets there is an alarm initiated. Any info will be appreciated.
_________________________
Bill
Top
2017 / 2014 NEC & Related Books and Study Guides
#101378 - 03/13/07 10:10 AM Re: Smoke detectors in HVAC ducts
rad74ss Offline
Member
Registered: 04/19/04
Posts: 156
Loc: Pryor, OK USA
I can't site a specific code but the equipment my company manufactures requires the entire smoke circuit to be operated off of a dedicated fire circuit. That includes the fire/smoke detectors, CO detectors, smoke purge and blower interlocks. If there is an outlet somebody is going to plug a drill into it eventually and depending on the fuse or circuit breaker size pop the circuit.

Edited out CO2 I must have been craving a soda.
Top
#101379 - 03/13/07 11:37 AM Re: Smoke detectors in HVAC ducts
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
NFPA 72 requires:

"Fire alarm systems shall be provided with at least two independent and reliable power supplies, one primary and one secondary." and:

"Connections to the light and power service shall be on a dedicated branch circuit." and:

"The OC device shall have a red marking, shall be accessible only to authorized personnel, and shall be identified as 'FIRE ALARM CIRCUIT CONTROL'."
_________________________
Earl
Top
#101380 - 03/13/07 11:39 AM Re: Smoke detectors in HVAC ducts
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Also, that would be CO detectors, not CO2.
_________________________
Earl
Top
#101381 - 03/14/07 09:45 PM Re: Smoke detectors in HVAC ducts
Elviscat Offline
Member
Registered: 08/13/05
Posts: 214
Loc: Seattle Washington USA
would a CO2 detector be what they use to track gases that cause global warming? j/k
Top
#101382 - 03/15/07 04:52 AM Re: Smoke detectors in HVAC ducts
ghost307 Offline
Member
Registered: 05/09/05
Posts: 899
Loc: Chicago Illinois USA
CO is what they're concerned with; carbon monoxide is much more deadly than carbon dioxide (although they're both bad news in the appropriate concentrations).
_________________________
Ghost307
Top
#101383 - 03/17/07 06:41 PM Re: Smoke detectors in HVAC ducts
Mark20 Offline
Member
Registered: 03/17/07
Posts: 25
Loc: Maryland
be sure the power source isn't gfi protected (760.21)
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals