#101331 - 03/07/07 06:35 PM Dishwasher/Disposal
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can a dishwasher with a nameplate amp rating of 8.7 amps and a disposal with an amp rating of 6.7 amps be connected to the same 20 amp branch circuit?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#101332 - 03/07/07 06:46 PM Re: Dishwasher/Disposal
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
And why would that be a problem? I don't see anything near 20 amps on the circuit ,,,, even if you assumed continuous operation!

[This message has been edited by renosteinke (edited 03-07-2007).]
Top
#101333 - 03/07/07 08:30 PM Re: Dishwasher/Disposal
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Depends on the manufacturer specifications. I'd check those first. As long as there is no lighting load on the circuit, I say you're good to go!

422.10 (B)
210.23 (A)(2)
Top
#101334 - 03/08/07 10:08 AM Re: Dishwasher/Disposal
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Disposals are on for such a short amount of time, they're unliky to ever trip a breaker, irregardless of whatever else is on the circuit- you could already have a 22A overload on that 20A circuit and still never trip it with a disposal.

In your case, I certainly don't see a problem sharing a dishwasher and disposal. In my house, I have the microwave sharing the circuit, too- the duty cycles are so short with so little simultaneity, it's just not a problem. (It wasn't completely intentional or I would have used two circuits... I simply forgot the dishwasher until it was too late to add a new circuit!)
Top
#101335 - 03/08/07 06:28 PM Re: Dishwasher/Disposal
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
Check for a local amendment. I've seen cities require separate circuits for the DW and disposal.

steve
Top
#101336 - 03/08/07 08:53 PM Re: Dishwasher/Disposal
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Why would they do that, stamcon?
Top
#101337 - 03/09/07 03:07 AM Re: Dishwasher/Disposal
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thank you for the replies...

I have always installed a seperate circuit for each appliance, but do not remember why I had been taught to or if it was a code requirement.

I found 430.53(A)which seems to apply?

shortcircuit
Top
#101338 - 03/09/07 09:19 AM Re: Dishwasher/Disposal
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
430.53 (A) will not help you here because both of your motors are over 1 horsepower. And 430.53 (A)(1) specifically does not allow motors over 6 amps.

1 HP = 746 watts

6.7 amps x 120 volts of alternating current = 804 watts
8.7 amps x 120 volts of alternating current = 1044 watts

Hope that helps you.
Top
#101339 - 03/09/07 10:05 AM Re: Dishwasher/Disposal
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
dishwashers also have a heating element; they are not a strictly motor load
_________________________
Earl
Top
#101340 - 03/09/07 01:28 PM Re: Dishwasher/Disposal
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Shock, don't let that 746w per horsepower thing confuse you. That is a theoretical number. You have to use the nameplate rating or 430.148.
I doubt the dishwasher has more than 1/4hp motor in it and I bet it is smaller. The 8.7a reflects the 1kw heating element and the timer. The disposal is probably 1/2hp, maybe 3/4.
I agree 430.(A)(1) seems to prohibit it but that conflicts with 210.23(A)(2). I also agree with Steve that this will probably never cause a problem and it is not a danger to the 12ga conductors but the AHJ will have to agree with that too.
The more I read the more confused I get. Simply the wording of the first sentence of 430.53(A) is contradictory.
"Several motors, each not exceeding 1 hp in rating, shall be permitted on a nominal 120-volt branch circuit protected at not over 20 amperes", but a 3/4hp motor is 7.6a.
_________________________
Greg Fretwell
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals