The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#101331 - 03/07/07 06:35 PM Dishwasher/Disposal
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can a dishwasher with a nameplate amp rating of 8.7 amps and a disposal with an amp rating of 6.7 amps be connected to the same 20 amp branch circuit?

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#101332 - 03/07/07 06:46 PM Re: Dishwasher/Disposal
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
And why would that be a problem? I don't see anything near 20 amps on the circuit ,,,, even if you assumed continuous operation!

[This message has been edited by renosteinke (edited 03-07-2007).]

Top
#101333 - 03/07/07 08:30 PM Re: Dishwasher/Disposal
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Depends on the manufacturer specifications. I'd check those first. As long as there is no lighting load on the circuit, I say you're good to go!

422.10 (B)
210.23 (A)(2)

Top
#101334 - 03/08/07 10:08 AM Re: Dishwasher/Disposal
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Disposals are on for such a short amount of time, they're unliky to ever trip a breaker, irregardless of whatever else is on the circuit- you could already have a 22A overload on that 20A circuit and still never trip it with a disposal.

In your case, I certainly don't see a problem sharing a dishwasher and disposal. In my house, I have the microwave sharing the circuit, too- the duty cycles are so short with so little simultaneity, it's just not a problem. (It wasn't completely intentional or I would have used two circuits... I simply forgot the dishwasher until it was too late to add a new circuit!)

Top
#101335 - 03/08/07 06:28 PM Re: Dishwasher/Disposal
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
Check for a local amendment. I've seen cities require separate circuits for the DW and disposal.

steve

Top
#101336 - 03/08/07 08:53 PM Re: Dishwasher/Disposal
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Why would they do that, stamcon?

Top
#101337 - 03/09/07 03:07 AM Re: Dishwasher/Disposal
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thank you for the replies...

I have always installed a seperate circuit for each appliance, but do not remember why I had been taught to or if it was a code requirement.

I found 430.53(A)which seems to apply?

shortcircuit

Top
#101338 - 03/09/07 09:19 AM Re: Dishwasher/Disposal
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
430.53 (A) will not help you here because both of your motors are over 1 horsepower. And 430.53 (A)(1) specifically does not allow motors over 6 amps.

1 HP = 746 watts

6.7 amps x 120 volts of alternating current = 804 watts
8.7 amps x 120 volts of alternating current = 1044 watts

Hope that helps you.

Top
#101339 - 03/09/07 10:05 AM Re: Dishwasher/Disposal
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
dishwashers also have a heating element; they are not a strictly motor load
_________________________
Earl

Top
#101340 - 03/09/07 01:28 PM Re: Dishwasher/Disposal
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Shock, don't let that 746w per horsepower thing confuse you. That is a theoretical number. You have to use the nameplate rating or 430.148.
I doubt the dishwasher has more than 1/4hp motor in it and I bet it is smaller. The 8.7a reflects the 1kw heating element and the timer. The disposal is probably 1/2hp, maybe 3/4.
I agree 430.(A)(1) seems to prohibit it but that conflicts with 210.23(A)(2). I also agree with Steve that this will probably never cause a problem and it is not a danger to the 12ga conductors but the AHJ will have to agree with that too.
The more I read the more confused I get. Simply the wording of the first sentence of 430.53(A) is contradictory.
"Several motors, each not exceeding 1 hp in rating, shall be permitted on a nominal 120-volt branch circuit protected at not over 20 amperes", but a 3/4hp motor is 7.6a.
_________________________