The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101313 - 03/06/07 04:42 AM Derating in Equipment
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Is it necessary to derate cables when installed within equipment, like switchboards or equipment cabinets? It seems silly to think that if I pop up and run, say, 3 cables each through 4 conduit sections consisting of two elbows joined end-to-end, I can use 100%, but if I run the 12 cables directly from one cabinet to the next (>24" total length), and strictly adhere to 310.15(B)(2)(a) I have to derate 50%, or even more considering the other cables in this equipment. I know I could pretend they're spaced, or separate them at points to pretend they're only bundled for 24" at a pop, but I'm pragmatic enough to know that's not meeting the intent of the code, and I'm far more interested in safety than I am in technicalities.

Are there special rules covering cable troughs and equipment that allow for lesser derating for short cables in equipment?

[This message has been edited by SteveFehr (edited 03-06-2007).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#101314 - 03/06/07 08:20 AM Re: Derating in Equipment
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
The NEC, in general, applies only to the "house" wiring, and not to the insides of equipment. After the disconnect, you're on your own.

This is not always as simple as it sounds. Take the example of an assembly line - many machines wired to act as one. One might argue that the NEC stops at the main control panel; yet, one would also be foolish to ignore the NEC for the power feeds to the sundry motors.

One NEC provision, in particular, can be tricky to follow: the ban on conductors passing through motor starters. Complex machines are often so interconnected that it's impossible not to have control wires going everywhere. At some point that collection of equipment has to become a single "appliance."

In short, there's still a role for professional judgment.

Top
#101315 - 03/07/07 04:01 AM Re: Derating in Equipment
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
I have a question about derating also. I have raintight trough outdoors, I go throught the wall and LB up to a trough indoors, the total length of the conduit penetrating the wall including the LB is less than 2 feet, derate or not??

Top
#101316 - 03/07/07 08:59 AM Re: Derating in Equipment
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Ah, just found a nice paragraph I'd never noticed- 366.23(A) allows us to ignore derating when there are less than 30 conductors in a sheet metal auxillery gutter. No exception for plastic, though. Very handy exception that could be easily extended to apply internal cabling inside most cabinets, I'd think.

Walrus,

310.15(B)(2) allows you to ignore derating factors on cables < 24" not in raceways, but gives no such exception for cables in raceways.

Copper cables act as their own heat sinks, transferring heat within the cable. Annex B.310.15(B)(3) goes more in depth into this, allowing you to use the greater ampacity if the higher derating factor is no greater than 10% of the run (max 10'). Which is VERY handy! Unfortunately, Annex B only applies to engineers, though, sorry! At any rate, this isn't additive with other exceptions, but the engineering rationale that the 24" bundle/nipple, cable gutter, etc, exeptions are based on.