#101274 - 03/02/07 08:00 AM auto xfmers questions
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 178
Loc: nc
Hey we have a dicussion here in the shop. I`m wiring a machine 380 volts 3phase. Well The rated kw reads as follows 380@70kw max.
I get 2 25kva xfmers and wire per 575/380 output my total figured kva is 103. Ok that`s my total avalible if needed.Co-workers maintain I should figure wire size and ocp according to 103 but I`m only using 70 of the 103 and plan on sizing accordingly.Also now here`s one thing we`re all unclear about in the auto configuration would we say 70kw/380x1.732=106amps
or use 70kw/575x1.732=70amps? Thanks in advance.
Top
2017 / 2014 NEC & Related Books and Study Guides
#101275 - 03/02/07 11:14 AM Re: auto xfmers questions
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 178
Loc: nc
I`m thinking that the voltage is 380 to the machine so I`m planning on going with 106amps calc. 125 ocp 1/0 wire thhn.
Top
#101276 - 03/03/07 12:43 PM Re: auto xfmers questions
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals