The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101267 - 02/28/07 08:24 AM extension cords
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
What code(s) prevent the use of extension cords for appliances, lamps etc. Please be as specific so as to convience this "lawyer" his refer. in his dining room must no be on a cord.. Thanks -dave

Top
2014 / 2011 NEC & Related Books and Study Guides
#101268 - 02/28/07 08:34 AM Re: extension cords
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Without starting an argument I think it is safe to say extension cords can NOT be used for fixed in place equipment. (the easy example is an orange cord running up to a garage door opener). Beyond that it starts geting hazy. The intent of 210.52(A) is to avoid extension cords but I am not sure how you stop the end user from extending a switched outlet around the wall to a lamp with a listed extension cord.
_________________________
Greg Fretwell

Top
#101269 - 02/28/07 08:49 AM Re: extension cords
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
590.3(B) restricts temporary cabling to a maximum of 90 days in this case.

400.8(1) is oft cited, as extension cords are most often used because there's no receptacle within 6' of where it should be. Also, the cords used are almost always too small- if you're using a cheap #18 extension cord on a 20A outlet, you're violating 400.5. As I work in a government office, they flat out forbade extension cords as illegal, and issued surge supressors with 12' cords instead! (Surge supressor is a device, which makes it not an extension cord, and therefore legal.) Letter the law vs intent of the law, I guess.

[This message has been edited by SteveFehr (edited 02-28-2007).]

[This message has been edited by SteveFehr (edited 02-28-2007).]

Top
#101270 - 02/28/07 10:07 AM Re: extension cords
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I may have been involved in the issue Steve is talking about if these were the cords in computer rooms. The determining factor from the safety standpoint is these "approved" surge strips also provide overcurrent protection. It was determined that a strip with O/C protection and no surge protection would also be OK but the NEC specifically allowed the ones with surge protection
_________________________
Greg Fretwell

Top
#101271 - 02/28/07 11:05 AM Re: extension cords
George Offline
Member

Registered: 02/23/02
Posts: 380
Extension cords are legal.

In fact, they are made for just the purpose the person wishes to use them for.

Top
#101272 - 03/01/07 08:49 AM Re: extension cords
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
Thank you! 400.8 was what I was looking for--dave

Top
#101273 - 03/02/07 02:48 PM Re: extension cords
hankj Offline
Junior Member

Registered: 08/14/05
Posts: 4
Loc: Browns Valley, CA, USA
Show him 210.52 (B)(1), then 400.8! If he doesn't get it then, he must really be my neighbor!

Hank