The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (jraef, LongRunner), 188 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#101225 - 02/26/07 12:40 PM Legality of Shore Power Cable
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Are shore power cables legal to use for temporary power connections, like to connect portable generators to a switchboard while the main building generators are undergoing mainenance/upgrade? NEC seems silent on the matter- would it rely completely on the UL listing? They're perfectly suited for this, though- flexible, tough, watertight, weathertight, etc.

By the same token, could other UL listed cable (like welding cable) be used in permanant installations? I've seen it done and been told it was legal, but never pressed the issue.

Top
2014 / 2011 NEC & Related Books and Study Guides
#101226 - 02/26/07 01:14 PM Re: Legality of Shore Power Cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Steve,
 Quote:
By the same token, could other UL listed cable (like welding cable) be used in permanant installations?

You can't use welding cable unless it has a dual listing as building type wire. Some welding cable is also listed as RHH and you can use that. There is also type W power cable that is very much like welding cable and it can be used per the rules in Article 400.
_________________________
Don(resqcapt19)

Top
#101227 - 02/26/07 01:32 PM Re: Legality of Shore Power Cable
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Speaking of "temporary" installations, what is the time period that temporary is good for? Specifically, when I worked on a movie set, welding cables were used to hook up portable distribution centers to installed building wiring. These cables were left installed for about 9 months. The facility was not a theater but a former manufacturing / warehouse structure.

Top
#101228 - 02/26/07 04:44 PM Re: Legality of Shore Power Cable
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Larry, the NEC defines temporary as 90 days or less.

Don, I agree with your answer, but not the reasoning.
When an issue comes up, I check the UL "White Book" for a little more clarification as to what the listing means.

In the case of welding cable, UL states that it is only rated for 100 volts, unless marked differently.

Then there is the issue of connectors. Most lugs and connectors are only evaluated for use with "ordinary" stranded wire. Very finely stranded wire ... welding cable, locomotive cable, whatever ... require connectors that are designed for use with them. In 'practical' terms, the approved connectors will have two set screws, bouble length barrels, etc.

[This message has been edited by renosteinke (edited 02-26-2007).]

Top
#101229 - 02/26/07 08:49 PM Re: Legality of Shore Power Cable
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
One other thing about welding cable is it is destroyed by U/V. I found this out on my boat
_________________________
Greg Fretwell

Top
#101230 - 02/27/07 02:25 AM Re: Legality of Shore Power Cable
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Don, I agree with your answer, but not the reasoning.


John I do not understand.

Welding cable is not (generally) listed as building wire.

If it is not listed in article 400 we can not use it.

The portable power cables we can use are listed in 400 and I think it goes without saying that you must use the proper terminals.

As far as I know the proper terminals are compression terminals, I don't think any lug that the set screw contacts the fine strands is listed for that use.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#101231 - 02/27/07 04:22 AM Re: Legality of Shore Power Cable
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Type W cable is listed in article 400 as going up to 1000kcmil, which is the size shore power cable I'm talking about, not just some #10 extention cord for a portable generator. 400.7 (B) which requires plugs does give an exception, "as permitted in 368.56" which allows direct bus connections for hard-usage.

If welding cable is cross-rated as class W, then 400.7 does appear to permit the uses I've seen it in, which is good news for me!

I believe the shore power cable I have availible is THOF/MIL-915. I've found a couple references to UL 44, RHH & RHW-2 in the catalog entries for these cables, but I don't know if those are universal throughout the industry or just happen to be what those particular manufacturers have done.

Follow-up question: if "Shore Power Cable" is RHW-2, is it exempt from cableway requirements for temporary installations? I don't see RHW-2 listed in Article 400. Where is RHH/RHW discussed? (Curse my non-searchable paper copy of NEC!)

Top
#101232 - 02/27/07 05:00 AM Re: Legality of Shore Power Cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
John,
 Quote:
In the case of welding cable, UL states that it is only rated for 100 volts, unless marked differently.

Most of the welding cable used around here is rated for 600 volts, but the UL listing says that the cable is only listed for use on the secondary side of electric welding machines. That being said I think that this is another bogus issue. I looked into using some Type "W" power cable for a temporaty installation a few years ago and found that in the case of one manufacturer the only difference between their Type W power cable and their welding cable, other than the listing and price, was that the welding cable had an insulation that was 25% thicker than the power cable. The stranding, strand count, and insulation type was identical. After finding that information, I went ahead and used the welding cable. Note this may not be true for all brands of cable, but it was true for the brand that I used.

Don
_________________________
Don(resqcapt19)

Top
#101233 - 02/27/07 05:06 AM Re: Legality of Shore Power Cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Larry,
 Quote:
Specifically, when I worked on a movie set, welding cables were used to hook up portable distribution centers to installed building wiring.

I think that would not be an Article 590 installation. It would be covered by 530. In a quick look, I did not see a time limit for the portable wiring on a movie set. However, listed cables and cords are required and welding cable would not be permitted.
Don

[This message has been edited by resqcapt19 (edited 02-27-2007).]
_________________________
Don(resqcapt19)

Top
#101234 - 02/27/07 05:09 AM Re: Legality of Shore Power Cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Steve,
 Quote:
Follow-up question: if "Shore Power Cable" is RHW-2, is it exempt from cableway requirements for temporary installations? I don't see RHW-2 listed in Article 400. Where is RHH/RHW discussed? (Curse my non-searchable paper copy of NEC!)

RHW is a building wire. See Table 310.13.
Don
_________________________
Don(resqcapt19)

Top