The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (hyetal), 262 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101171 - 02/14/07 08:22 AM main breaker or not?
royta Offline

Registered: 09/03/04
Posts: 136
Loc: CA
I've always been confused on whether I need a main breaker for a sub-panel.

Situation 1 - Residential main service with a feeder breaker feeding sub-panel mounted within or on home. Is there a situation when the sub-panel needs a main?

Situation 2 - Residential main service with a feeder breaker feeding sub-panel mounted on seperate structure or somewhere else on property. Sub-panel only needs a main IF there are more than six breaker handles (twin counts as two handles), correct?

Situation 3 - 400A residential main service with first 200A main supplying the built-in distribution. Second 200A main feeding 20/40 sub-panel located on other side of house. Sub-panel has conduit provisions to supply future sub-panels located on other structures or areas of property.

Situation 4 - Commercial main service on exterior of building. Individual feeder (main) breakers feeding sub-panels located in each commercial suite. Every sub-panel I've ever seen in these situations always has a main breaker.

[This message has been edited by royta (edited 02-14-2007).]

2014 / 2011 NEC & Related Books and Study Guides
#101172 - 02/14/07 08:49 AM Re: main breaker or not?
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
1. Not needed

2. Needed if six disconnects are exceeded. A 2 pole breaker is one breaker. If by twin you mean a breaker with two separate handles, then the twin counts as two.

3. Not needed

4. Not needed
Few things are harder to put up with than the annoyance of a good example.