#10107 - 05/30/02 09:32 PM Conductors in Parallel
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
Is there a code stating the maximum number of conductors allowed to be paralleled. I know 1/0 is minimum size but found no limit on how many. I want to use four 350KCM per phase instead of two 1000KCM. Kinda tough to work that fat stuff into the bottom fed switchgear.
Top
Work Gear for Electricians and the Trades
#10108 - 05/31/02 10:27 AM Re: Conductors in Parallel
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Four conductors per phase can be used under NEC 310-4, if the equipment is intended for 4 cdr/ø. Keep lengths equal and similarly routed for each group. If 1000kcmil is specified and there’s code-adequate bending space, use it! Won’t kill you.
Top
#10109 - 05/31/02 02:06 PM Re: Conductors in Parallel
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
I don't think there is a Maximum number as long at the terminations are made to accept the number of the parallel conductors.

Going from a bus to a bus I would think is virtually unlimited.

To devices such a Circuit Breakers the available (listed) lug pattern for that CB would be the determining factor.
Top
#10110 - 05/31/02 05:40 PM Re: Conductors in Parallel
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
I don't believe their is a maximum # of parallel conductors, as long as they meet the conditions of 310.4 ('02), or 310-4 ('99)
Top
#10111 - 05/31/02 06:53 PM Re: Conductors in Parallel
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
I have never heard of a maximum. The more you do the harder it gets to keep them all "the same length" I have had the pleasure [said with much sarcasm] of terminating 12 runs of 500MCM paralleled myself. (And 10 runs of 600 MCM come to think of it) It is really not that bad IF you have sufficient room and you realize you are not going to finnish before lunch the day you start. (you probably won't finnish before lunch the following day either!)
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals