The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 88 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#101020 - 01/31/07 10:34 AM double up
skipper Offline
Junior Member

Registered: 01/22/07
Posts: 6
Loc: dartmouth ,mass
in the code does it state that on a main breaker you can not put two wire into the same screw connector on the load side

2014 / 2011 NEC & Related Books and Study Guides
#101021 - 01/31/07 12:05 PM Re: double up
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
The basic rule for connections to terminals is one terminal, one conductor. If the terminal is listed for more than one conductor, then you can put in as many as the listing states.

See 110.14 (A)
Few things are harder to put up with than the annoyance of a good example.