#100555 - 12/01/06 04:53 PM 400 Amp Service
gserve Offline
Member
Registered: 03/11/03
Posts: 92
Hi,I am an electrician that has done mostly residential work up to 200A service.I have a job that will require 400Amp service.Seeing I have never done one I am seeking any advise that you could give me.I have read that most of the time 2 200A panels are used.This project is a garage and I would like to use just 1 main panel.Is this impractical? Just looking for some guidance. Thanks in advance.
Top
2017 / 2014 NEC & Related Books and Study Guides
#100556 - 12/01/06 05:44 PM Re: 400 Amp Service
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If you use a single 400 amp panel in place of two 200s you will pay more money and have half the circuit space when it's done.

The last 400 home service I did I used a single 400 only because I had not yet seen a double 200 set up. If it comes up again I am going with double 200s.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#100557 - 12/01/06 06:10 PM Re: 400 Amp Service
Fred Offline
Member
Registered: 04/30/01
Posts: 449
Loc: Straughn, IN 47387
I use either a 320A metermain with (2)200A breakers installed to feed (2)200A 40ct ML panels or if they can be back to back with a 320A meterbase I use (2) 200A 40ct MB panels. I am currently upgrading a 320A service at a house to an 800A due to a 6500 sq.ft. addition. The PoCo is hitting my CT cabinet at the addition where it will feed a 800A ML panelboard with (1)400A CB to feed the old service and (2) 200A CBs to feed (2) 200A 42ct ML panels in the new addition. Houses around here keep getting bigger and stupider.
Top
#100558 - 12/02/06 09:30 AM Re: 400 Amp Service
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I always wonder how much of that 400a actually gets used. What are these people's electric bills? Average 60a 24/7 is over $1000 a month here.
_________________________
Greg Fretwell
Top
#100559 - 12/02/06 10:11 AM Re: 400 Amp Service
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
Quote:
I always wonder how much of that 400a actually gets used. What are these people's electric bills? Average 60a 24/7 is over $1000 a month here.


Generally speaking, in many places 400A service is the next step up if the load calc exceeds 200A. And, of course, the load calc is interested in making sure that the probable sustained peaks are covered; it's not about the average draw. So one might need a 400A service when the current draw averaged over the course of a month is only a few dozen amps or less.
Top
#100560 - 12/03/06 03:55 PM Re: 400 Amp Service
gserve Offline
Member
Registered: 03/11/03
Posts: 92
So it looks like I need a 1/O GEC for 400A service based on 600 kcml conductors. Do you normally parallel them with smaller conductors? Any help on the conductor size please. Also do they make a rebar clamp for the 1.5" rebar for the 1/O conductor size?
Top
#100561 - 12/03/06 04:04 PM Re: 400 Amp Service
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
4 AWG CU is the largest conductor you ever have to run to a concrete encased electrode.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#100562 - 12/03/06 04:11 PM Re: 400 Amp Service
gserve Offline
Member
Registered: 03/11/03
Posts: 92
Thanks Iwire. How about help with the service conductor sizing.If 600 kcml is required what 2 sizes do I need to parallel to make up this size?
Top
#100563 - 12/03/06 05:51 PM Re: 400 Amp Service
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Just a reminder to pay extra attention to your load calcs. If the calculated load is over 320 amps, then a different type of service - one with a current transformer- will be needed.
Top
#100564 - 12/03/06 06:38 PM Re: 400 Amp Service
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Reno- I believe that would be true if the 320a. were a continious load. He stated that this was a residential installation and residential is not continious. He could do the calc and come up with 400a. and if the equipment were rated for 400a. he's good to go.
_________________________
George Little
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals