#100364 - 11/15/06 01:59 PM recepts in tub area
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
A homeowner wants to install a flat screen TV over a tub. There is about a one foot 'deck' area between the tub and the wall on which the TV will be installed apx. three or four feet above the tub water level. The TV needs a recept (behind the TV) for power.

This is tub only, not a shower.

Is this installation allowed?
Top
2017 / 2014 NEC & Related Books and Study Guides
#100365 - 11/15/06 02:14 PM Re: recepts in tub area
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
680.71 would apply, I believe, and thus this installation is allowable as long as the TV manufacturer doesn't say the TV can't be in this area.

Sound good?
Top
#100366 - 11/15/06 02:29 PM Re: recepts in tub area
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
No it does not sound good, it sounds incredibly bad and I would not do it for them.

Take a look at 406.8(C)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#100367 - 11/15/06 02:42 PM Re: recepts in tub area
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Is it permissible to daisy-chain 3 GFCI receptacles in a row, just to make doubly/triply sure it's going to work?
Top
#100368 - 11/15/06 03:22 PM Re: recepts in tub area
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Code wise you can daisy chain an infinite number of GFCIs.

You still can not put a receptacle in the tube area.

You also are not supposed to pass cords through walls.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#100369 - 11/15/06 06:13 PM Re: recepts in tub area
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Do we have a difinition of "tub area"? I've always understood "tub space" was the footprint of the tub or shower and up to the ceiling?
Edit to add the following comment: I see a lot of jobs where the deck around the tub is rather large and I've not had a problem with a receptacle in the tub "area" that I could quote a code section for a violation. Tough call. Always ask for GFCI protection. In the "tub or shower space" - no receptacles.

[This message has been edited by George Little (edited 11-15-2006).]
_________________________
George Little
Top
#100370 - 11/18/06 10:19 AM Re: recepts in tub area
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
680.71 clearly allows recepts less than five feet from the inside walls of the tub with GFCI protection. So the question is (as already said) what is the definition of 'tub area'? If it's the one, two, or three walls and ceiling that surround the tub, then would it be acceptable to put a recept just around the corner of a wall and run the cord around the wall and plug it in?

What about free standing tubs? What is that tub area?

Unfortunately, I think 680.71 throws a real kink in 406.8(C).
Top
#100371 - 11/18/06 11:12 AM Re: recepts in tub area
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
680.71 is under the heading for hydromassage tubs.
All the general use electronic equipment I have seen has a warning to keep it away from water.
The only installation I ever saw that looked safe was where they built a closet at the end of the tub with a window into the bathroom. The T.V and receptacle were in the closet and the owner used a remote control.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top
#100372 - 11/27/06 05:39 PM Re: recepts in tub area
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
What does keeping something 'away from water' mean?
Top
#100373 - 11/27/06 05:44 PM Re: recepts in tub area
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
I think someone should propose similar wording from 410.4(D) for 406.8(C).

2011 here we come.
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 95 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals