#100327 - 11/11/06 09:21 AM Pull Box v. Junction Box
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
If I have 2 inch conduit entering one side of a box and exiting with a 2 inch directly across from the conduit entering the box we have a straight pull. Right? If the conductors are AWG #4 or larger the box needs to be at least 16 inches between conduit entries hence at least a 16 inch box. (NEC 314.28(A)(1) '05 Ed.) Now- if I splice these conductors can I reduce the size of the box to 12 inches based on (2)?

Edited for spelling

[This message has been edited by George Little (edited 11-11-2006).]
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#100328 - 11/11/06 10:36 AM Re: Pull Box v. Junction Box
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
George,
A splice doesn't change anything. If the conduit goes straight it is 8 X and if the conduit goes out a wall at 90° it is 6 X.
Don
_________________________
Don(resqcapt19)
Top
#100329 - 11/11/06 11:26 AM Re: Pull Box v. Junction Box
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Don- I agree with you put you'll get arguements if the conduits are offset or if there is a splice. I think it should be made clearer somehow. I ask for a 16 inch box.
_________________________
George Little
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals