The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
49 minutes 28 seconds ago
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 252 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#100327 - 11/11/06 09:21 AM Pull Box v. Junction Box
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
If I have 2 inch conduit entering one side of a box and exiting with a 2 inch directly across from the conduit entering the box we have a straight pull. Right? If the conductors are AWG #4 or larger the box needs to be at least 16 inches between conduit entries hence at least a 16 inch box. (NEC 314.28(A)(1) '05 Ed.) Now- if I splice these conductors can I reduce the size of the box to 12 inches based on (2)?

Edited for spelling

[This message has been edited by George Little (edited 11-11-2006).]
George Little

2014 / 2011 NEC & Related Books and Study Guides
#100328 - 11/11/06 10:36 AM Re: Pull Box v. Junction Box
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
A splice doesn't change anything. If the conduit goes straight it is 8 X and if the conduit goes out a wall at 90┬░ it is 6 X.

#100329 - 11/11/06 11:26 AM Re: Pull Box v. Junction Box
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don- I agree with you put you'll get arguements if the conduits are offset or if there is a splice. I think it should be made clearer somehow. I ask for a 16 inch box.
George Little