The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#100324 - 11/10/06 06:36 AM Space Heater calculations
WhiteRook Offline

Registered: 02/17/04
Posts: 49
Loc: Republic of Texas
I am looking at a job installing 4 electrical space heaters with fan forced air(hung in the red iron) in a 16000 sq ft unfinished strip mall. The units are 7.5 Kw. The house panel is 208/120 3-phase with 150A main. The spec sheet lists the units as drawing 27A for 208 3-phase. When I was figuring the load, 7500 divided by 360, I get I correct in figuring the difference in amperage is for the fan portion? I believe the code states that fixed electric space heaters (Art. 424.3(B)are to be considered continuous loads. So would I need 35A breakers for this? And if I put the branch circuit wiring for 2 of these heaters in one conduit the derating for the 7 wires at 70% would mean that I would have to run #6??? If I put all four in one conduit from the panel to a pull box inside then @13 wires I would have to run #4??? This doesn't even take in to account voltage drop. So what do ya'll think, am I right or am I confused.

2014 / 2011 NEC & Related Books and Study Guides
#100325 - 11/10/06 12:12 PM Re: Space Heater calculations
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
I get 6 wires (80%) and 12 (still 50%), you don't count the neutral where it only carries unbalanced current and you never count grounds for derating, only fill.
Greg Fretwell

#100326 - 11/10/06 03:14 PM Re: Space Heater calculations
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I don't think there is a neutral Greg. Maybe he's running an EGC. In either case I agree with your numbers.