The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 211 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#100324 - 11/10/06 06:36 AM Space Heater calculations
WhiteRook Offline
Member

Registered: 02/17/04
Posts: 49
Loc: Republic of Texas
I am looking at a job installing 4 electrical space heaters with fan forced air(hung in the red iron) in a 16000 sq ft unfinished strip mall. The units are 7.5 Kw. The house panel is 208/120 3-phase with 150A main. The spec sheet lists the units as drawing 27A for 208 3-phase. When I was figuring the load, 7500 divided by 360, I get 20.83A...am I correct in figuring the difference in amperage is for the fan portion? I believe the code states that fixed electric space heaters (Art. 424.3(B)are to be considered continuous loads. So would I need 35A breakers for this? And if I put the branch circuit wiring for 2 of these heaters in one conduit the derating for the 7 wires at 70% would mean that I would have to run #6??? If I put all four in one conduit from the panel to a pull box inside then @13 wires I would have to run #4??? This doesn't even take in to account voltage drop. So what do ya'll think, am I right or am I confused.

Top
2014 / 2011 NEC & Related Books and Study Guides
#100325 - 11/10/06 12:12 PM Re: Space Heater calculations
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I get 6 wires (80%) and 12 (still 50%), you don't count the neutral where it only carries unbalanced current and you never count grounds for derating, only fill.
_________________________
Greg Fretwell

Top
#100326 - 11/10/06 03:14 PM Re: Space Heater calculations
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I don't think there is a neutral Greg. Maybe he's running an EGC. In either case I agree with your numbers.