The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (Radar, LongRunner), 224 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#100287 - 11/08/06 01:20 PM Light Pole Grounding
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
Hey Everybody,

I'm arguing with a low-ball lighting installer about the need for poles to be grounded as well as the luminaires on 12' parking lot lights. The installer seems to think that the mechanical link between the pole and the luminaire is sufficient, so only the luminaire needs to be grounded. I call BS and reference 410.15 (specifically, 410.15(B)(5)) and feel that the code specifies that any metalic pole, 8' or higher, needs to be bonded to ground using the grounding bolt welded to the inside of the hand hole, and using the manufacturer-supplied (and UL listed) gounding hardware. The luminaire, of course, must be grounded ALSO.

My logic is that if, for some reason (corrosion, a hit from a moving truck, etc.), the luminaire becomes detached from the pole, or the mechanical link becomes comprimised in any way, the pole then becomes a possible conductor when/if a fault occurs. Add one barefooted kid leaning on the pole, and we have a tragedy that could have been easily avoided.

BTW, this guy came in to one of the communities that I service and underbid my company on the pole replacements by using "immigrants of questionable legality" to perform the work for him. There was never, to my knowlege, a certified or licensed electrician on site during the entire process. And yes, I may be a little biased in my motives on this issue.

Does anybody think that I'm out of line on this, or am I right? Are there any inspectors here that have run across this issue and made the call either way?

Thanks in advance for your input.

Top
2014 / 2011 NEC & Related Books and Study Guides
#100288 - 11/08/06 01:59 PM Re: Light Pole Grounding
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Zapped, I agree with you, 410.15(B)(5)is mighty clear in requiring the pole to be bonded to an EGC.

Roger

Top
#100289 - 11/08/06 02:39 PM Re: Light Pole Grounding
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Well, the way I see it, even if it was not required to be bonded, The bonding conductor is present and running right past the bonding stud up to the fixture, so why not just take the extra 30 seconds and bond the pole anyway. For the time and material it might take, its peanuts and
" cheap insurance" compared to what the price may be if someone were to get hurt or killed because the pole somehow became hot.

A.D

Top
#100290 - 11/09/06 04:20 AM Re: Light Pole Grounding
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Zapped:
YES, poles MUST be bonded. This discussion was recently had regarding a "fail" sticker I posted on a site lighting project.

John
_________________________
John

Top
#100291 - 11/09/06 07:08 AM Re: Light Pole Grounding
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
Thank you gentlemen, it's nice to have some back-up when you know you're right.

It's difficult to beleive what people will argue with you about sometimes.

BTW, sorry for double posting Roger. Thanks for handling that!

Top
#100292 - 11/09/06 11:10 AM Re: Light Pole Grounding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
As a design issue I would like to see the bonding conductor being a bit longer than the circuit conductors so it would break last in a collision.
_________________________
Greg Fretwell

Top
#100293 - 11/09/06 11:54 AM Re: Light Pole Grounding
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Gfretwell:
Sounds plausable.....
Most of the impacts I have dealt with have resulted in some spectacular fireworks; either upon impact, or the 'maintenance guy' trying to reset the 3-pole cb.

John

[This message has been edited by HotLine1 (edited 11-09-2006).]
_________________________
John

Top
#100294 - 11/09/06 12:30 PM Re: Light Pole Grounding
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Zapped, no need for an appology.


Roger

Top
#100295 - 11/10/06 06:57 AM Re: Light Pole Grounding
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
gfretwell: I wholeheartedly agree with the extra ground wire length.

I've been the guy to go out a secure the sites after poles have gone down, and more than once I've found the wire over extended to the point of failure, and have found more than one has become a 4" X 4"X 20' steel conductor. I've always been glad that I found it before a someone else.

Around here, it's becoming a real problem. So called "lighting" speciallty contractors are entering into the market and are practicing predatorial bidding to get into a job, then using unqualified labor in order to turn a profit on an impossibly low bid. The result? The customers get what they pay for. And IMHO, it's scary, and it will not end well.