#100227 - 11/01/06 06:55 AM MC Cable/ Concrete bsmt. wall
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What are the inspectors saying about using MC cable, (interlocked) installed for a drop for a laundry plug etc. when it is in contact with a masonry wall? No PVC jacket on the cable and does it need physical protection? Maybe I'm too strict. I say no way.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#100228 - 11/01/06 08:34 AM Re: MC Cable/ Concrete bsmt. wall
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
So long as it is dry and secured properly, I see no problem. If there is a concern with physical protection, sleeve it in EMT or PVC.
_________________________
Earl
Top
#100229 - 11/01/06 08:35 AM Re: MC Cable/ Concrete bsmt. wall
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
What is your concern, what do you cite and what would you accept? RNC uses the same "physical damage" language.
Do you want it on a running board (corrosion issue) or do you want it sleeved in RMC?
_________________________
Greg Fretwell
Top
#100230 - 11/01/06 08:37 AM Re: MC Cable/ Concrete bsmt. wall
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Dean, most MC is listed "wet" these days. It has dual rated THHN/THWN conductors in it.
_________________________
Greg Fretwell
Top
#100231 - 11/01/06 08:46 AM Re: MC Cable/ Concrete bsmt. wall
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What about the aluminum jacket?
_________________________
George Little
Top
#100232 - 11/01/06 08:55 AM Re: MC Cable/ Concrete bsmt. wall
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
What's wrong with the aluminum jacket? Is your concern a reaction with the block wall or a damage issue?
I am still curious what your cite is.
I know "damage" is a local call and the local practice varies widely across the country, even from AHJ to AHJ in the same general area. In Md it is common to simply staple Rx on running boards in utility areas. In this area of Florida that is not OK but they will take ENT (smurf). Other areas set the minimum at EMT.
I have not heard about concerns about MC, one way or the other.



[This message has been edited by gfretwell (edited 11-01-2006).]
_________________________
Greg Fretwell
Top
#100233 - 11/01/06 09:52 AM Re: MC Cable/ Concrete bsmt. wall
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg- I guess that's why I posted the issue. I know we can't have aluminnum wire in contact with concrete. I would not have a problem if they ran it MC on a running board. Guess I'm getting paranoid in my old age
_________________________
George Little
Top
#100234 - 11/01/06 04:14 PM Re: MC Cable/ Concrete bsmt. wall
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I may have a problem with aluminum wire used as a Ufer. I am not sure there is a concern about simply having aluminum against concrete. We have aluminum screen cages tapcon screwed to the slab and the block walls out in the weather. I have not seen any corrosion issues with them and that is here in monsoon country. I think I would be more concerned with steel straps on aluminum armor but that doesn't seem to be an issue.
_________________________
Greg Fretwell
Top
#100235 - 11/01/06 04:26 PM Re: MC Cable/ Concrete bsmt. wall
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I went back and looked at the references to concrete and aluminum. It says you can't pour the raceways in the concrete without supplimental protection and references "chlorides" that may be in the concrete <handbook note>. That is usually calcium chloride "heat" they put in to speed up the setting.
_________________________
Greg Fretwell
Top
#100236 - 11/01/06 05:30 PM Re: MC Cable/ Concrete bsmt. wall
steve ancient apprentice Offline
Member
Registered: 03/04/05
Posts: 169
Loc: west springfield,mass
Here in mass we usually rum nm stapled to a running board. I see no problem with mc on the masonary but if your concerned shoot a board and then clamp the mc to the board. Can even sleeve romex thru emt with the changeover. The cheaper way out than useing mc.Mc can be for exposed work. I dont have a problem with what you are doing.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals