Question : Is a bonding bushing required when you have 277 volt wiring going through 1/2" liquidtight flexible metal conduit ( sealtight). This is terminated into a 4 square box that has concentric / eccentric knock outs. The knock outs are 1/2" to 3/4" with only the 1/2" taken out. I say yes a bonding bushing is required as per 250.97 another electrician say no you don't need them because its sealtight not a metal raceway like rigid conduit.
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
But LFMC is a metal raceway and in some cases can be used as the EGC. I've read 250.97 and 350.60 and 250.118 (C) and my educated guess would be YES, a bonding bushing is needed if this run is more than 6.'
I look forward to reading more replies on this matter but I have to leave for school now.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
IMHO you win the beer. Unless the box is listed to provide the required bonding with only the 1/2" ko removed. Some of them are.
George Little
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I see it the same as George.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
OK, add a another agreement
John
John
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
According to the UL white book, all outlet boxes (such as four inch) are suitable for bonding over 250 volts, without additional bonding, even with concentric.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Thanks Ryan, I thought I'd read that somewhere but I wasn't sure so I appreciate that info as does everyone else on this BB.