Can a receptacle be placed directly behind a kitchen or bathroom sink? I have always taken that the 24" and 36" are measured from the edge of the basin. Therefore to me the area inside the edges were restricted.

Any thoughts?
Thanks
_________________________
Joe Rossi
Top
2017 / 2014 NEC & Related Books and Study Guides
#100201 - 10/27/06 12:35 PM Re: Receptacle Placement
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Joe- the answer is yes to both locations. As a matter of fact the graphic in the '05 code even illustrates it for a kitchen sink. I've always had reservations about locating a receptacle on the wall behind a cooktop above the cooktop but I can't see any restrictions on that either. One could use the inspectors judgment that it would be subject to physical damage (heat) but I guess the inspector could be correct. The other part of the question might be- What would you use it for? That's right there with the restriction on puting a receptacle in a shower (Prohibited by code unless listed for that purpose) I don't even want to know what you'd use a receptacle in a shower for.
_________________________
George Little
Top
#100202 - 10/27/06 12:46 PM Re: Receptacle Placement
JoeRossi Offline
Member
Registered: 01/31/03
Posts: 26
Loc: Washington, NJ
Thaks, if you look at the illustration of Figure 210.52 it shows space behind the sink. I came across a sink with about 2" of counter top behind it and a receptacle directly behind the facut. I felt it would be more dangours if someone wanted to use it. Other than a safety factor, I do not see any code that would inhibit it.
_________________________
Joe Rossi
Top
#100203 - 10/27/06 02:06 PM Re: Receptacle Placement
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
We do have a little bit of a safety net here with GFCI protection required for these locations.
_________________________
George Little
Top
#100204 - 10/27/06 02:45 PM Re: Receptacle Placement
yanici Offline
Member
Registered: 09/03/06
Posts: 58
Loc: Atlantis
I was on another forum where a member wrote in. He was on a job for a guy who had a large rental complex. It seems that this owner wanted a receptacle on the wall directly above each electric range. He couldn't seem to get how a cord would end up in the soup. The electrician was trying to appease this guy because he gave them a lot of work. Never did hear the final outcome.
Top
#100205 - 10/27/06 03:03 PM Re: Receptacle Placement
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Ughck! Amperage flavored soup!

I have never in my life seen a receptacle placed directly above an oven range on purpose.
Top
#100206 - 10/27/06 06:12 PM Re: Receptacle Placement
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They used to sell elecgric ranges with a NEMA 5-15 receptacle built in.
_________________________
Greg Fretwell
Top
#100207 - 10/27/06 06:30 PM Re: Receptacle Placement
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Code doesn't consider the sink to be countertop space, so I'd tend to think that a receptacle behind the sink, while not prohibited, might not count towards the 24/48" requirement. Kinda splitting hairs there, though.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals