ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
#100083 10/16/06 11:05 AM
Joined: Apr 2002
Posts: 178
R
Member
When building a system when would you choose 3 ph over single or vice versa. We`re putting in some equipment into a textile plant where they have 3 phase 600 volt I`ve noticed some three phase 600 to 120/240 transformers and some single phase 600/120/240.We`re installing a small panel with mostly 120 volt loads for small equipment and some lighting. Thanks in advance.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#100084 10/16/06 11:29 AM
Joined: Dec 2003
Posts: 751
E
Member
Generally speaking, use 3 phase whenever it is available. For the cost of one additional conductor, you increase the capacity of the panel by a factor of 1.73(over single phase).

But, if you consider the cost of the minimum size allowable panel (often 100 amps) versus the cost of a 3 phase 100 amp panel, AND, if the total load to be used can be handled by the single phase 100 amp panel, then that is the most economical choice. (As is the case in residential services.)

In your case, the industrial load may not be sufficient to warrant the additional cost. The question you need to ask is: Who is paying the bills, and do we want to plan for any future loads?


Earl
#100085 10/16/06 02:39 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Unless you need the 3 phase for some equipment there is no point in having a "120/240/" 3 phase system. I say that because you will not be able to use the high leg for anything on 120v. or 240v. single phase. If you have a 208/120 3 phase you could use all three legs.

And since I'm being picky the term is 240/120v. for 3 phase and 120/240v. for single phase per IEEE dictionary.

Finger don't tipe rite. [Linked Image]



[This message has been edited by George Little (edited 10-16-2006).]


George Little
#100086 10/16/06 06:03 PM
Joined: Jun 2005
Posts: 821
S
Member
Quote
the term is 240/120v. for 3 phase and 120/240v. for single phase per IEEE dictionary.

See that? I learn something new everyday here.

Thanks!

#100087 10/16/06 06:16 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The basic, and informal, method is:
On single phase list the low voltage first, like: 120/240 and 120/208

On three phase list the high voltage first, like: 480/277, 240/120, and 208/120

A letter Y is usually added for wye systems - 208Y/120 or 480Y/277.

#100088 10/21/06 05:58 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Quote
the term is 240/120v. for 3 phase and 120/240v. for single phase per IEEE dictionary.

Any idea how far back this convention goes?

#100089 10/21/06 07:38 AM
Joined: Sep 2006
Posts: 111
E
Member
240/120 3 phase? I always thought you can only get 208/120 from 3 phase?

#100090 10/21/06 08:53 AM
Joined: May 2002
Posts: 1,716
R
Member
Eddy, the 240/120 3 phase is a Delta Configuration of windings with one winding center tapped for the grounded conductor whereas the Wye configuration is tapped at the end of three windings.

This is why only two legs/phases of the Delta will give you 120 and all three phases of the Wye will give you 120.

Scott has some good information and drawings of these transformer configurations in the Technical area.

Roger

#100091 11/01/06 06:41 PM
Joined: Oct 2006
Posts: 4
E
Junior Member
"Unless you need the 3 phase for some equipment there is no point in having a "120/240/" 3 phase system. I say that because you will not be able to use the high leg for anything on 120v. or 240v. single phase."

This is partly true. With a high leg delta system you have 240V between any two phases, so you could use the high leg and one other to run a 240V single phase appliance (if the breaker is rated to handle the high leg voltage).

[This message has been edited by EASports (edited 11-01-2006).]

#100092 11/01/06 07:06 PM
Joined: Jan 2004
Posts: 1,507
G
Member
EASports- Be careful-
Quote
This is partly true. With a high leg delta system you have 240V between any two phases, so you could use the high leg and one other to run a 240V single phase appliance.
You need to look at 240.85, especially the latter part of the text. Unless that breaker you are referring to has a straight 240v. rating, you would not be able to use it on a single phase 240v. circuit using the high leg. Some breakers have a slash rating- 120/240 and they could not be used on the high leg of a 3Ø 240/120v panel if they are accross the high leg. Common violation.