The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (jraef, LongRunner), 188 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#100023 - 10/05/06 09:33 AM Transformer
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
OK I deal mostly residential but on a 3 phase xfmer 600v to 220/120 15kva Can someone bring back to basics. I have approx 39.3 amps on each phase correct?

Top
2014 / 2011 NEC & Related Books and Study Guides
#100024 - 10/05/06 10:03 AM Re: Transformer
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
FLA on a 15 kva at 208 is 15/(0.208 x 1.73)= 41.6 amps.

Top
#100025 - 10/05/06 10:53 AM Re: Transformer
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Thanks Bob after further review it actually was 208/120 secondary.Thanks again.41.6 it is.