OK I deal mostly residential but on a 3 phase xfmer 600v to 220/120 15kva Can someone bring back to basics. I have approx 39.3 amps on each phase correct?
Top
2017 / 2014 NEC & Related Books and Study Guides
#100024 - 10/05/06 10:03 AM Re: Transformer
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
FLA on a 15 kva at 208 is 15/(0.208 x 1.73)= 41.6 amps.
Top
#100025 - 10/05/06 10:53 AM Re: Transformer
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 178
Loc: nc
Thanks Bob after further review it actually was 208/120 secondary.Thanks again.41.6 it is.