#100 - 11/25/00 09:16 AM ground wire and rods
doc Offline
Member
Registered: 11/25/00
Posts: 119
Loc: Texas
at a seperate building even if you run a ground with your wiring do you still have to install a ground rod at the seperate building
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Top
Work Gear for Electricians and the Trades
#101 - 11/25/00 06:25 PM Re: ground wire and rods
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
A grounding electrode system is always required at the second building unless it only has one branch circuit feeding it. See 250-32(a)
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top