#205259 - 02/08/12 08:09 AM
Balcony
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
I have a question and I don't know if it was asked before. If you have a balcony as per 210.52(E)(3) and you have handrail that goes right up to the door frame, How are you suppose to mount a receptacle and still be within the perimeter of the balcony?
|
|
Top
|
|
|
|
#205262 - 02/08/12 08:42 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
No side walls? No 'wall' space at all? Option #1 might be a suitable raceway and a receptacle mounted to the rail. Can I say ugly?
Or, hope it is less than 20 square feet, per the exception.
_________________________
John
|
|
Top
|
|
|
|
#205265 - 02/08/12 10:25 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 11/27/07
Posts: 729
Loc: MA, USA
|
IMO, in building construction terms anyway, an area of that minimal size at the top of the stairs, which it sounds like your describing, would generally be considered a landing and part of the staircase, so probably not an actual balcony in the traditional sense or as mentioned in the NEC.
|
|
Top
|
|
|
|
#205268 - 02/08/12 11:15 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
If you need to make it pretty, have the rail fabricator box in the first pair of rail balusters, up a foot or so and set an FS box in there. Then you can hide the raceway/cable where it enters the wall next to the door frame. Do it on the side opposite of the door opening (on the hinge side or pocket side) so the cords will be away from the traffic path.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#205272 - 02/08/12 02:42 PM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Under circumstances where there could be a trip/safety issue, I would have no issue granting a variation for NO receptacle. Gregs solution will work, IF someone spends some $$$.
_________________________
John
|
|
Top
|
|
|
|
#205321 - 02/10/12 11:29 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
Greg,
What happens if it is wrought iron railing?
|
|
Top
|
|
|
|
#205322 - 02/10/12 11:30 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
John,
This is a question an EC asked me, he also asked me if I would fail him for NOT putting a receptacle out there?
|
|
Top
|
|
|
|
#205324 - 02/10/12 11:56 AM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
Wrought Iron might be the easiest to deal with since you could just bridge the balusters with a steel enclosure and paint it to match the railing. Tougher would be some fancy power coated aluminum rail.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#205326 - 02/10/12 01:19 PM
Re: Balcony
[Re: harold endean]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Harold: The answer would be it's your call as AHJ. IF the balcony is under 20 Sq ft, the exception solves the situation.
If it's over 20 sq ft, you may consider a variation application, with substantiation that is acceptable to you.
However, I would add that the substantiation has to be enough to CYA. The variation may be considered a precedent that could be referenced by others.
Gregs solution sure sounds like the best idea, but without 'seeing' the job, we may all be guessing.
_________________________
John
|
|