#177768 - 05/11/08 08:55 PM
Re: A puzzel for Henry C
[Re: gfretwell]
|
harold endean
Member
Registered: 02/16/02
Posts: 1047
Loc: Boonton, NJ
|
Offline
|
|
My 2 cents on this puzzle. If the breaker was OFF and the GFI receptacle had power but tripped the test/trip buttons on the receptacle, then the breaker must be defective.
If the breaker was OFF and you couldn't rest the test/trip buttons on the GFI receptacle, maybe you needed power in order to reset the buttons on the receptacle.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177771 - 05/11/08 09:07 PM
Re: A puzzel for Henry C
[Re: harold endean]
|
twh
Member
Registered: 03/11/04
Posts: 257
Loc: Regina, Sask.
|
Offline
|
|
It must be interesting or it wouldn't be posted here. I'll guess hot and neutral reversed.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177786 - 05/12/08 06:36 AM
Re: A puzzel for Henry C
[Re: EV607797]
|
SteveFehr
Member
Registered: 03/19/05
Posts: 926
Loc: Chesapeake, VA
|
Online
|
|
It was tripping from current through the neutral and a neutral-ground fault.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177799 - 05/12/08 12:34 PM
Re: A puzzel for Henry C
[Re: Alan Nadon]
|
venture
Member
Registered: 01/08/06
Posts: 33
Loc: San Diego Ca USA
|
Online
|
|
Panel connections wrong/bad? Rod
|
|