#177616 - 05/08/08 02:11 PM
Spliced Neutral?
|
jkochan
Member
Registered: 01/19/05
Posts: 57
Loc: Phoenix, AZ USA
|
Offline
|
|
We opened a panel in our commercial building this morning to trace a few circuits. While in there, I found that one of the neutrals on a branch circuit had been spliced. It is a soldered connection and insulated with what looks like heat shrink tubing. It looks as though a GFCI breaker was removed and a standard 20A breaker installed in it’s place, and they spliced the neutral to reach the bus. Is this legal? Do I have to re-pull this incredibly long branch circuit to correct it or could this be considered a repair to a “damaged neutral”?
Edited by jkochan (05/08/08 02:12 PM)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177658 - 05/09/08 09:57 AM
Re: Spliced Neutral?
[Re: electure]
|
renosteinke
Moderator
Registered: 01/22/05
Posts: 3063
Loc: Reno Nv USA
|
Online
|
|
I think some clarification is necessary.
Solder is a perfectly acceptable method - but not just solder alone. Where solder is used, the wires must have some other means physically holding the wires together - such as twisting them together. Solder will make the 'electrical' connection; the 'mechanical' must come from elsewhere.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177667 - 05/09/08 12:08 PM
Re: Spliced Neutral?
[Re: electure]
|
SteveFehr
Member
Registered: 03/19/05
Posts: 890
Loc: Chesapeake, VA
|
Offline
|
|
Heat shrink does not meet 110.14(B) regardless of thickness, as it is applied after the splice is soldered, vice before. Seems a pretty nitpicky point, though. Is twisting the wires sufficient, though? If so, the heat shrink may only be required to function as electrical insulation. Not sure how you'd check up on that.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177690 - 05/09/08 07:58 PM
Re: Spliced Neutral?
[Re: SteveFehr]
|
renosteinke
Moderator
Registered: 01/22/05
Posts: 3063
Loc: Reno Nv USA
|
Online
|
|
Steve, I'm not sure I follow you. Tape is a proper means of insulation, and it's certainly applied 'after' the splice is made. I don't have any problem with heat shrink tube as covering for a splice.
I would have a problem is the tube was left with an open end. Otherwise, use it.
For the mechanical connection, twisting the wires is generally enough. Sure, there are exceptions ... where you need to use a hydraulically crimped or welded connection ... but for most purposes, twisting is plenty good.
Naturally, for larger wire (like you might see used in a service), the practice is not to simply try to twist the wires, but rather to braid the strands together. There's an entire art to these splices, that's pretty much been lost.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177697 - 05/10/08 08:29 AM
Re: Spliced Neutral?
[Re: renosteinke]
|
mikethebull
Junior Member
Registered: 03/18/07
Posts: 17
Loc: Rhode Island
|
Offline
|
|
I thought tape was not UL approved to "replace" the original insulation. That was why you have rubber tape and then a outer layer of electrical tape. But why wouldn't the person(s) just have used a wirenut. Seems to me that they must have been "nervous" about electricity, probably a handyman special.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177700 - 05/10/08 11:05 AM
Re: Spliced Neutral?
[Re: mikethebull]
|
renosteinke
Moderator
Registered: 01/22/05
Posts: 3063
Loc: Reno Nv USA
|
Online
|
|
All electrical tape, of whatever form, pretty much has to pass the same tests. The only real variable is the voltage rating - and that's based upon only a two-layer thickness.
"Ordinary" electrical tape is listed for 600v. So are the usual splicing tapes and putties. The 'self fusing' nature of the splicing tapes does make the final set waterproof, and the thickness is a real help to building up thickness.
There are reasons for building up some thickness, apart from electrical insulation. For example, to cover sharp edges.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |