#177564 - 05/07/08 03:32 PM
Instant Under counter Hot Water Heaters
|
Yoopersup
Member
Registered: 03/04/03
Posts: 447
Loc: Michigan
|
Offline
|
|
Instant Hot water heater under the sink Bradford model EFT-28000-4-T-10 208 volt single phase. Draws close to 140 amps. Theres 45 units that theses are POSSIBLY going to be installed. As far as I see it each one must be rated for condutious duty(X125%)45 x 6075x125% aprox 760 amps ??? Anyone know of any derateing ect in this case?? Seem like a lotta power for Hot water??? Yoopersup
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177566 - 05/07/08 06:03 PM
Re: Instant Under counter Hot Water Heaters
[Re: Yoopersup]
|
electure
Moderator
Registered: 12/24/00
Posts: 3627
Loc: Fullerton, CA USA
|
Offline
|
|
Article 100 defines continuous load as:
"A load where the maximum current is expected to continue for 3 hours or more"
That's one heck of a long time to run the sink.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177569 - 05/07/08 07:23 PM
Re: Instant Under counter Hot Water Heaters
[Re: electure]
|
Yoopersup
Member
Registered: 03/04/03
Posts: 447
Loc: Michigan
|
Offline
|
|
So Hot water Heaters don't need the 125 % either???? 422.13 ?????? come into play
Edited by Yoopersup (05/07/08 07:25 PM)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177573 - 05/07/08 08:14 PM
Re: Instant Under counter Hot Water Heaters
[Re: Yoopersup]
|
electure
Moderator
Registered: 12/24/00
Posts: 3627
Loc: Fullerton, CA USA
|
Offline
|
|
The water heater is not a storage type. It is an "On Demand" type.
It heats the water when needed, and only when needed.
Here's a PDF If you scroll down to "Series Three" you'll find it there. http://www.bradfordwhite.com/images/shared/pdfs/specsheets/217b.pdf
Edited by electure (05/07/08 08:17 PM) Edit Reason: I forgot to addlink
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177575 - 05/07/08 09:01 PM
Re: Instant Under counter Hot Water Heaters
[Re: electure]
|
Yoopersup
Member
Registered: 03/04/03
Posts: 447
Loc: Michigan
|
Offline
|
|
So where does it deal with Demand type in the NEC?? and whats to stop it from being on for three hrs or more???? (I knew it was demand type Thus the product #)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177578 - 05/07/08 10:03 PM
Re: Instant Under counter Hot Water Heaters
[Re: Yoopersup]
|
renosteinke
Cat Servant
Moderator
Registered: 01/22/05
Posts: 3100
Loc: Reno Nv USA
|
Offline
|
|
Yooper, I might see a few errors in your thinking.
These are single-phase 'whole house' water heaters. I assume that means that these will each be going in a different residence, and different panels.
Does the load seem high? Sure - that's the price you pay for 'instant' heat.
When you do the load calcs for multiple dwellings, there's a multiplier for your "diversity factor." The effect of this is, whether you use the 125% figure or not in each individual panel, I don't think it will change the final total service needed.
Looks like you need 3 two-pole breakers - and they;ll need to be mounted next to each other, so they can be considered as disconnects 'grouped together.'
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177630 - 05/08/08 07:36 PM
Re: Instant Under counter Hot Water Heaters
[Re: renosteinke]
|
Yoopersup
Member
Registered: 03/04/03
Posts: 447
Loc: Michigan
|
Offline
|
|
I called the Company your right, Three 2 pole 40 amp breakers for each unit . and thats the Minimin size they say would be required to feed a, Shower, Bathroom sink, Kitchen sink combo. Becta there not going in!!!.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177647 - 05/09/08 06:39 AM
Re: Instant Under counter Hot Water Heaters
[Re: Yoopersup]
|
SteveFehr
Member
Registered: 03/19/05
Posts: 923
Loc: Chesapeake, VA
|
Offline
|
|
It's insane how much power it takes to heat water on demand, isn't it? I would have had to upgrade my service to put in an in-use hot water heater for my home. Gas isn't much better- the size gas like you need for even a 1-shower-at-a-time tank line that is obscene, too.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
Moderator: resqcapt19, Roger, iwire, Ryan_J, Trumpy, Scott35, renosteinke, pauluk, LK, electure, dougwells, C-H
|
|