#177191 - 04/24/08 04:18 PM
How to bleed the capacitance charge off of 13.8 kV
|
salty
New Member
Registered: 04/24/08
Posts: 3
Loc: Washington, USA
|
Offline
|
|
Can anyone explain how to bleed the capacitance charge off of 13.8 kV wires so I can do work on the transformer? The transformer is a GE (model GEI-79025M) and we are using 600 Amp dead break connectors (3M 5815 Series). The dead break connectors have capacitive test point in the dead end plug but it is not conductive so I cannot use it to bleed the capacitance charge. I cannot use a hot stick to remove the dead break connector because they are the bolt on type. The 13.8 kV feed is an underground loop system going from one transformer to the next, with a total of 16 transformers.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177193 - 04/24/08 06:21 PM
Re: How to bleed the capacitance charge off of 13.8 kV
[Re: salty]
|
JoeTestingEngr
Member
Registered: 11/04/05
Posts: 569
Loc: Chicago, Il.
|
Offline
|
|
Doesn't the utility usually take care of that when they open and ground the lines? Joe
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177194 - 04/24/08 06:46 PM
Re: How to bleed the capacitance charge off of 13.8 kV
[Re: JoeTestingEngr]
|
salty
New Member
Registered: 04/24/08
Posts: 3
Loc: Washington, USA
|
Offline
|
|
No. We are performing the function of the utility using inside wireman.
Edited by salty (04/24/08 06:48 PM)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177196 - 04/24/08 08:17 PM
Re: How to bleed the capacitance charge off of 13.
[Re: salty]
|
Trumpy
Cat Servant and
Moderator
Registered: 07/05/02
Posts: 7375
Loc: South Island, New Zealand
|
Offline
|
|
What you need is someone competent enough to do this sort of work. Using in-experienced staff will end in disaster. HV work is not like any other sort of electrical work, it is a totally different animal!
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177448 - 05/03/08 12:41 AM
Re: How to bleed the capacitance charge off of 13.
[Re: HighPotter]
|
Trumpy
Cat Servant and
Moderator
Registered: 07/05/02
Posts: 7375
Loc: South Island, New Zealand
|
Offline
|
|
High-Potter, Your post asks more questions than it actually answers. Electrical Contractor.Net shall not be responsible for any advice given with respect to HV equipment and lines if something should go wrong. Having un-qualified people working on HV gear is just asking for trouble! Advice like this is NEVER given over the NET, you haven't even seen the installation and are going on a guys word. You want to take that responsibility on?
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177449 - 05/03/08 02:15 AM
Re: How to bleed the capacitance charge off of 13.
[Re: Trumpy]
|
Check Pilot
Member
Registered: 11/25/05
Posts: 118
Loc: Edmonton Alberta Canada
|
Offline
|
|
Mike,
Although your advice is, as usual, superbly astute, and I know most experienced sparkies reading this thread will understand it, I know and understand that capacitance discharge can kill ya really quickly, I can only say that for the original question is to cut off and then let the capacitors self discharge for at least 12 hours before going anywhere them. The only answer is to cut the feed to all the transformers for at least 12 hours before servicing the stuff.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177452 - 05/03/08 04:38 AM
Re: How to bleed the capacitance charge off of 13.
[Re: Check Pilot]
|
Trumpy
Cat Servant and
Moderator
Registered: 07/05/02
Posts: 7375
Loc: South Island, New Zealand
|
Offline
|
|
Dave, I just have a problem with folks that are not conversant with HV work, as in clearances and PPE. It only takes one hit with a HV voltage to bring you to your knees and kill you. Be careful, is all I can say.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177466 - 05/03/08 01:13 PM
Re: How to bleed the capacitance charge off of 13.
[Re: Trumpy]
|
renosteinke
Cat Servant
Moderator
Registered: 01/22/05
Posts: 3100
Loc: Reno Nv USA
|
Offline
|
|
I have avoided this thread .... simply because HV stuff is beyond my competence.
Were I asked to work on HV gear, my answer is simple: NO. If I were told it was part of my job, I would insist on training ... and the training ought to be more than 'take this tool in there and twist the widget." Anyone who claims it's simple, any moron can do it - let them show you!
As an example, I recall the time the PoCo had to kill a transformer to a grocery store. After swinging the cover open, there was a plain steel panel, with only a simple switch handle visible. Did they just flip the handle? NO. The put on PPE, extended the hot stick, and turned the handle from 10 ft. away! One has to conclude that there were reasons for these precautions.
When it comes to HV, I don't even know how to flip a switch!
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#177469 - 05/03/08 03:54 PM
Re: How to bleed the capacitance charge off of 13.
[Re: Trumpy]
|
HighPotter
Member
Registered: 08/29/04
Posts: 41
Loc: So. Cal
|
Offline
|
|
High-Potter, Your post asks more questions than it actually answers. Electrical Contractor.Net shall not be responsible for any advice given with respect to HV equipment and lines if something should go wrong. Having un-qualified people working on HV gear is just asking for trouble! Advice like this is NEVER given over the NET, you haven't even seen the installation and are going on a guys word. You want to take that responsibility on? So Im confused here. Do you disagree with the method I discribed, or that advice given at all?
There are grown men on this board, who are professionals, and who post serious topics. You should either remove the "offending" original post, or open the topic up for discussion. ( And then you will get opinions from poster) Situations like this ARE discussed over the net on a daily basis. Check out Powerlineman.com, Line-man.com. Heck even over on Mike Holt Forums. I field questions at work regarding high voltage situations, and I answer them and offer my opinion to the best of my ability. I will do the same here. Based on the posters specific situation, in no way did I offer "dangerous" advice. If you think I did, then I would be happy to discuss it. Email,phone...you name it.
HP
|
|